I agree with mort2376, I would swap over the MCB to 25A which would probably function ok at 3kw. Alternatively, run 2.5mm T&E between the two outlets and turn it into a ring or finally, split into 2 circuits at 16A each. But I wouldn't leave it as it is.
32A is standard protecton for a ring circuit, radial circuits should have 20A protection. This is to protect the wires. The ring circuit will be 2 sets of 2.5mm wires which together, are rated higher than 32A. Single 2.5mm twin and earth on a radial circuit is rated higher than 20A.