Welcome to Talk Electrician Forum, the UK's Friendliest Electrical forum on the internet, whilst you can view all our posts and topics like most online communities you must register to post (reply, or ask a question) in our community, but don't worry this is a simple free process that requires minimal information for you to signup. We do have different membership levels (called silver and gold) as a subscription service, BUT, this is an extra, and not needed, So please feel free to join for FREE, and then decide if you like our community, and would perhaps like to subscribe to any of our our extra services. Our members offer the best advice in the electrical industry including DIY,Domestic,Commercial,Industrial,Renewables,Health and Safety issues and Control and Automation.

Be a part of Talk Electrician Forum by signing in or creating an account.
  • Start new topics and reply to others
  • Subscribe to topics and forums to get automatic updates
  • Get your own profile and make new friends
  • Customize your experience here
Guest Message by DevFuse
 

Photo
- - - - -

New cooker install question.


  • Please log in to reply
10 replies to this topic

#1 wmoore

wmoore

    Junior Member

  • Bronze Member
  • 8 posts
Offline

Posted 14 August 2010 - 03:11 PM

We had a new cooker delivered the other day to replace an old one, but they would not wire it up for us because we did not have a terminal outlet box behind the oven. It seems the cable runs up behind the kitchen units into the control unit switch
and then off to the CU. (can't see behind kitchen unit)
The last oven was install 2 years ago so have the reqs changed in that time.
The old cooker was rated at 10.2Kw and the MCB at the CU was 32amp.
New cooker is rated at 8.7Kw
So do we have to get this terminal outlet box install or not ?
and is that 32amp MCB suitable or not.

thanks.

#2 bluetobits

bluetobits

    Member

  • Bronze Member
  • 83 posts
Offline

Posted 14 August 2010 - 03:21 PM

I'd go for a 10mm cable, 40amp MCB and fit a terminal outlet

#3 matt.leung

matt.leung

    Distinguished Member

  • Bronze Member
  • 1,038 posts
  • LocationBromley, Kent
  • Skills:Domestic, Commercial, Teaching
  • Training:Time Served
  • Employment:Self Employed
  • Country:United Kingdom
Offline

Posted 14 August 2010 - 03:25 PM

8700/230 = 37A, so 40A mcb needed

#4 wozz

wozz

    Distinguished Member

  • Bronze Member
  • 2,213 posts
  • LocationKent
  • Skills:Domestic, Commercial, Industrial
  • Training:Time Served, Apprenticeship
  • Employment:Self Employed
Offline

Posted 14 August 2010 - 03:35 PM

not using diversity then?

This happens alot where currys refuse to connect up for some reason or another.

call a electrician and ask them to wire it up, and follow manufactures instructions.

there may even be a electrician on here in your area.

#5 wmoore

wmoore

    Junior Member

  • Bronze Member
  • 8 posts
Offline

Posted 14 August 2010 - 03:49 PM

The cooker did not come with any cable.
The main question I am asking is.
Must I install a terminal outlet box when I am only changing the appliance over to a new one ?
And what is the purpose of said box ? I can understand having it if your cooker comes with it's own cable, but if it doesn't you need to buy extra cable.
The new cooker says it should be connected to an omnipolar switch with
HO5RR-F cable.

#6 Tooold

Tooold

    Senior Member

  • Bronze Member
  • 270 posts
Offline

Posted 14 August 2010 - 04:21 PM

Diversity on a cooker is, if memeory serves me, first 10amps then 30% of the remainder plus 5amps if cooker switch has a socket outlet on it. So 10amps plus 8 amps plus a possible 5 amps is 23 amps.
Of course the usual cable calcs have to be done.
The cable is a rubber appliance cable which is fine if big enough but there are other cables that would be good enough.
Cant help with cable calcs as havn't got my books with me.
I usually fit an outlet plate but I dont think its a must more of a reccomendation. I may be wrong though

#7 sparkytim

sparkytim

    Distinguished Member

  • Bronze Member
  • 1,755 posts
  • Country:United Kingdom
Offline

Posted 14 August 2010 - 05:06 PM

Currys delivery guys are not Electricians.

They are only allowed to connect to a Cooker connection unit which can be isolated at a suitable Cooker switch above.

Your 32 Amp and 6mm cable cooker circuit is adequate.

I would suggest installing a low level cooker connection point and this will solve any problems in the future.

#8 PC Electrics

PC Electrics

    Distinguished Member

  • Bronze Member
  • 1,980 posts
  • LocationClinging to the starboard bow
  • Skills:General All Rounder, Domestic, Commercial, Vehicle, DIY (Self Taught), Other
  • Training:Other
  • Employment:Self Employed
  • Country:United Kingdom
Offline

Posted 14 August 2010 - 05:11 PM

A cooker outlet point is defo "best practice" and I doubt any sparks wiring a kitchen these days would leave it out. However I come across 6mm t&e coming straight from the isolator to the appliance on many occasions. In these situations I usually add a 30A junction box and continue to the appliance with 4mm H07RN-F ( http://www.tlc-direc...TQ3slash50.html ), there's usually a cupboard or skirting to screw the JB to. H07RN-F will satisfy any manufacturers instructions. I also keep 2.5mm for smaller appliances (eg ovens). You don't say what size your instructions recommend (bear in mind 4mm might not fit - though that's unlikely on a cooker, usually only on ovens). You'll need cord end terminals (or you could tin the ends)

Your 32A/6mm circuit is plenty adequate for an 8.7kW cooker (seems small for a cooker though, would have thought the hob alone would have added up to that). The OSG says this size circuit is good for 15kW cooking appliances in domestic.

Alternatively, just connect the t&e straight into the cooker if that's the best you can do yourself.

#9 batty

batty

    Snoopy™

  • Gold Member
  • 10,998 posts
  • Country:United Kingdom
Offline

Posted 14 August 2010 - 07:44 PM

I have stopped putting in outlet plates especially in fitted units they are just a waste of time and another thing to go wrong but always leave enough cable so oven can be fitted easily. I have been out loads of times to people that have not had cookers fitted by the likes of currys etc just fit it on to the end of the cable job done.

#10 a1spark

a1spark

    Senior Member

  • Bronze Member
  • 604 posts
Offline

Posted 14 August 2010 - 08:05 PM

Hi wmoore. If thats what currys specify then thats what you will need, as Sparkytim states there delivery staff are only trained to connect to the low level outlet unit
AS you already have the cable running from the above worktop isolator down to the cooker position why not just install the outlet unit onto the end of it ...job done as they say !

#11 initforthemoney

initforthemoney

    Senior Member

  • Banned
  • 449 posts
Offline

Posted 15 August 2010 - 04:15 PM

F F S,

Allow me to answer directly....

YES you can connect directly to the existing cable and NO you dont HAVE to fit a connection point.

Your new cooker is rated less than the old, so it will be fine.