Bit confused on my test results for a cabin with its own tt earthing system
I have installed 2 circuits, lights and sockets.
R1+R2 on lights =0.04
R1+R2 on sockets = 0.05
insulation on both circuits >500
ZS on lights = 111.3
ZS on sockets = 111.8
ZE = 110.4
PFC 2a :(
PSC 509a
Why would the PFC be so low? I retested it to make sure I had a good connection but got the same result. Any advice would be very much appreciated
0
Share this post
Link to post
your PEFC is 2a for the simple reason of Ra being 110.4...
your PFC is the highest of PEFC and PSCC. in this case, 0.5KA. so its not low.
0
Share this post
Link to post
Meady
Your pefc is just the result of Volts Divided by your ze
so
Say you have 220 volts and a ze of 110ohms then your pefc will be 2 amps
regards chris
0
Share this post
Link to post
thanks for info, just been swatting up on it all and its all sinking in now, been a long day and a few beers needed now.
0
Share this post
Link to post
ZE = 110.4
PFC 2a :(
PSC 509a
All with RCD protection i take it ? :Pray
0
Share this post
Link to post
Yep, cabin on an rcbo