I was changing a CU today and didn't do an IR test before I started (that's a lesson learned). All went well until I started turning the new duel RCD board on.
I turned on the main switch and then the first RCD. I pressed the RCD test button like all good leccies should and nothing happened, the RCD didn't trip. All MCBs are off at this point.I narrowed the problem down to one of the lighting circuits on that RCD. If both the neutral and the CPC were connected in the board, the RCD test button didn't work and the RCD didn't trip at
or
.
I disconnected the circuit and found that there was continuity between the neutral and CPC.
Looked in lots of the light fittings until I found the problem, rectified it and all was good with the world again.
My question is, why would a properly working RCD not trip if there is a neural to earth fault, I would have thought it would trip all the time and not reset.
It seems that I don't understand RCDs. Anyone able to enlighten me?
Thanks
Hello Ali..
few observations and thoughts
1/ All MCB's off so even if power is on to the supply side of the RCD, there is no current flowing through the RCD yet cuz no loads switched on?
No current flowing so RCD wont trip even with a N-E fault present.
2/ If you had got some of your MCB's on with some appliances or lights switched on somewhere in the property I suspect the RCD would have tripped cuz current could now bypass the N half of the RCD through your N-E fault.
3/ Is the supply on the installation PME/TN-C-S..
i.e. Neutral and Earth joined together at the suppliers main cut-out?
cuz this will give you the symptoms you are describing:-
I will try & explain:-
Have a look at figure 11.1 on page 93 of the On-Site-Guide.
IF PME/TN-C-S, you can draw an connection between the N & E on the bottom left hand side of the drawing..
Now also put another connection between the N and E just before the load on the bottom right hand side of the drawing. (your N-E fault)
Remember the brown live wire from the RCD to the load would be open circuit because your MCB's are off..
Now lets consider a possible test current path...
- From Live
- Up the black wire to the test button
- Through the test button
- Through the test trip load resistor
(This is where it can now take two paths)- (i) Along the neutral through the RCD coil
or - (ii) Along the neutral wire toward the load
- (ii) Through your N-E fault
- (ii) Along the Earth wire
- (ii) Back from the Earth to the Neutral at the PME/TN-C-S connection.
If this is a PME/TN-C-S earth arrangement the two paths will probably be of a very similar resistance so the fault test current will most likely divide equally down the 'N' and the 'E'.
So the little bit of current flowing through the N coil of the RCD is probably too small to cause it to trip!
If Earth arrangement is TN-S or TT the resistance via your N-E fault down the earth conductor will be higher so the test fault current going down the E will be less..
So more will go down the N coil of the RCD and provide enough to trip the RCD with the test button!

hope that makes sense????