I have read with some interest the posts in this thread, it appears that there is some confusion on what the R1+R2 test is, what it can tell you and what readings you should expect.
The R1+R2 test is one of a number of tests used to verify the ring final circuit. The reading you get at the consumer unit for R1+R2 will be the same at each socket on the ring. If all conductors and cpc are of the same diameter say 2.5mm and you get end to end readings of say 0.50 then the R1+R2 readings would be approx half of this at 0.25. This is what you would expect at each socket, I have seen people come to me saying they have found a high reading at a socket and tell me its say 0.30 or a low reading of 0.20, in reality this could be expected and the variation is not enough to cause concern. A high reading of say 0.40 would require further examination, and a number of faults could be the cause. Normally if all the readings are within the parameters of the test results at all the sockets bar one, it could be a faulty socket, where the switching is not working correctly, or as previously discussed a spur.
The highest recorded reading is what goes onto the certificate. There is no furthest point on a final ring circuit, as the circuit could be broken at any point to test the R1+R2. The R1+R2 and end to end tests can also be used to calculate the circuit length,although not required to be included on the certificate it does give you an insight into how the cables are run when doing a periodic inspection.
R1+R2 testing is a dead test and your tester needs to be zero'ed in order to get correct readings, faulty readings could be down to contacts with the probes, low battery on tester or connections amongst others. When testing it is always a good idea of what you expect to see, and not just except what you record.