Is this allowed ??
To spur off the 2.5mm ring using 4mm cable. i.e. creating radial circuit from ring.
I thought spur off spur is not allowed??
Share this post
Link to post
6 answers to this question
  • 0
Although the 4mm can handle the current, you could be drawing from a point in the ring where you`d prospectively cause overload in one of the legs of the ring.
It`d be better to take the 4mm back to the CU, or feed 1 socket only; thereby negating the necessity for 2.5
HTH
KME
Share this post
Link to post
  • 0
a spur from a spur is a no no but you are asking can you take a spur from a ring and this is allowed.:D
Share this post
Link to post
  • 0
I would say that you should only feed the max of 1 double unless you come off the output side of a FCU sat on the ring.
While in theory the 4mm could take more points, what happens if the ring is spilt into 2 radials down the line, this will leave your bit plus what
Share this post
Link to post
  • 0
a ring is designed with a max draw of 13A at any point (or something like that). so although the 4mm can safely take the full 32A, you would be overloading a point on the ring, and if its close to one side, you could easily overload one leg of the 2.5
Share this post
Link to post
  • 0
If you spur off of a ring in 4mm
Share this post
Link to post
  • 0
My thoughts are its better to take a spur of ring in 4 mm than extend ringmain again and again. I have been to properties that have been extended where ringmain has been extended so much readings are of the scale. Although when I am doing extensions I put new circuits in unless its a real problem.