Sorry Steptoe, misunderstood, i beleive now you mean distance from a terminal to an opening.Ok
If its "Fanned Draught" the minimum distance is 300mm regardless of position.
If its "Natural Draught" then distance differs with position and rating of appliance.
Upto 7 KW 300mm regardless
7Kw - 14KW - 600mm above a terminal, 300mm below, 400mm horizontal
14KW-32KW - 1500mm above, 300mm below, 600mm horizontal
32KW-70KW - 2000mm above, 600mm below, 600mm horizontal
Though if this is a open flue appliance the above posts still need to considered, in your instance the appliance is not a open flue, so ignore the above.
A Promax is room sealed and fan draught, so minimum is 300mm