I'm revising for an exam and we haven't really done anything about transformers since before xmas. Can someone please check if I have done this calculation right?
"A transformer has 50 turns on the primary and 8 turns on the secondary. The primary is supplied at 600V. The output on the secondary will be...?"
Am i right in thinking it's (voltage of winding / number of turns) * amount of turns on the secondary? So (600/50)*8 = 96. So the output would be 96V?
If I'm wrong please tell me and I'll try to work it out. Thank you :)
Correct...  you just need to remember that....
Voltage Primary/Voltage Secondary = No Of Turns Primary/No Of Turns Secondary = Current Secondary/Current Primary..
So whatever values you are given use and transpose the bits accordingly..
BUT don't forget that the current ratio is arse about face to the others.. i.e  Secondary:primary  not Primary:Secondary.
Bottom line is (excluding small losses) the transformer does not generate or consume any power,
so if the Voltage goes down.. the current must go up.. so V*I remains equal on both sides..
(thats why need care with conductor sizes on low voltage lighting as 50W @ 230V  = 0.2A ish
but 50W @ 12v = 4A ish)
Guinness
+1.
As I drive about I am amazed at the long term reliability of these beasts.
Some have been in continuous service for at least 50 years within the
distribution network.