Been meaning to post this for a while but keep forgetting.

When filling out a PVT DC cert, under the Array Parameters we have Voc and Isc to fill out.

Been on 2 big contracts with contradicting requirements.

One says to put in the parameters of ONE panel, so for example 10 x 255 panels would still be Voc - 37.4 and Isc - 8.98

The other say to multiply the Voc by the number of panels. So the same example would be Voc - 374 and Isc still 8.98.

So, which, if either is correct?

Thanks

 
So it's the second example. That was my thought, like you said, it states array parameters NOT module parameters.

I argued this with the latest contractor but they want it for single module. Another case of 'do as your told and NOT as you please'.

Thanks for confirming

 