hi all hope your all well, I'm new here and thought it would be a good place to ask this question that most will find easy to answer but has me thinking.
I picked a book up called electrical calculations at my local college and thought i would borrow it. I come across this question and didn;t seem right to me
The design current of a circuit protected by a BS 1361 fuse is 28A. The grouping correction factor is 0.8 and the ambient correction is 1.04. Calculate the minimum current carrying capacity of the cable.
Well the answer is 36.5 but i managed to get 36.4 every time, just wondering if any one else can get 35.5?
Its a book i never heard or seen before and thought i would have a bit of bed time reading and come across some very strange questions.
I picked a book up called electrical calculations at my local college and thought i would borrow it. I come across this question and didn;t seem right to me
The design current of a circuit protected by a BS 1361 fuse is 28A. The grouping correction factor is 0.8 and the ambient correction is 1.04. Calculate the minimum current carrying capacity of the cable.
Well the answer is 36.5 but i managed to get 36.4 every time, just wondering if any one else can get 35.5?
Its a book i never heard or seen before and thought i would have a bit of bed time reading and come across some very strange questions.