Extractor Fan Control - Wiring Size


gembrain

Question

Got a ceiling mounted extractor box that controls/powers an external extract fan via a plug in connector. The extractor box is supplied by 1.5mm cable with a fused isolator.

 

Connecting it to a Solar and Palau TD500 fan - max consumption 50w.

 

Does this part classify as a "control circuit" so 0.75mm flex OK or does it need to be 1mm for an appliance?

 

No requirements stated by either the extractor box manufacturer or the fan manufacturer.

 

Thanks.....

Link to comment
Share on other sites

3 answers to this question

Recommended Posts

I have no idea, but you are talking about a few pence per metre difference for the larger cable so i would just fit it.


Not knowing any exact spec 50W only needs a very small dia cable, how long will the cable run be ?

Link to comment
Share on other sites

Cable run all of 3 metres. No insulation involved.

Have some .75mm 4 core heat resistant which theoretically would be fine - just wanted to save myself a trip out :)

Link to comment
Share on other sites

.75mm would be fine for the fan but depending on the size of fuse it might be worth checking it would make disconnect times in the case of a fault. 