Hotel In Single Phase

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

gozzer66

Junior Member
Joined
Dec 15, 2009
Messages
25
Reaction score
0
Hello. Ive recently been working in a hotel in N Wales, was asked to look into why a 12kw water heater was tripping the mcb, it was 32 amp run in 6mm. Told him to change to 10mm and 50amp etc. When i looked more closely at the supply intake, discovered that the whole 5 bed hotel is single phase and protected by a 60amp main fuse. There are electric showers in all the rooms, electric cooker and all the usual ring mains and lights etc. I advised changing the water heater to 7.5 kw and looking into getting 3 phase brought to the hotel. They reckon that they have been there 10 years and never had a problem. The main fuse seal has been renewed ?when, the old seal is broken and left on top of meter. I was going to look inside main fuse carrier to see what is in there. Does anyone think this is an odd situation or have any thoughts.

 
Diversity is king.

but if all 5 rooms take a shower at the same time, while the breakfast is cooking in the kitchen.......

Note the make of CU. If it's handling that without catching fire, then THAT is what we should all be fitting, not this metal clad stuff with the same carp fittings inside.

 
Tails are 25mm, PME supply.

M2 breakers (cef) no markings visible on both cu

 