250Mtr Drive Way Lighting
Dave4718
Feb 3, 2011
24
Hi
I have been asked to light up a driveway using lime trees to fix lights to, my dilemma is the distance from supply to end of line. I have a good board to provide a supply and the customer wants it stringing between trees which are 4 mtrs apart. Voltage drop is the obvious consideration, the calculator suggests 16mm cable. Is there a suitable stabilizer to do the job or do I need to look at low voltage. The lamps will be something like 8w LED I was hoping to get away with 1.5/2.5 SWA
 any ideas would be appreciated.
Dave
if the lighting is spread out then you can get away with small cables as you go, but still, 250mtr is a long drive. of course, you could be lucky and the meter be at the far end with submain to house...
Can I throw an "out of the box" idea.
A string of 20, 12V lamps in series. (yes think big set of christmas tree lights)
Just a thought. Now shoot me down in flames. (don't ask me where you would measure VD)
Are these going both sides of the driveway or just one? Either way if thats absolutely what the client wants then a 4mm swa each side with the fittings tee'd off it would be the sort of idea id be going for. Although spending that amount of money and sticking the lights in trees rather than other solutions seems daft.
Hi
Dave
i would sugest doing the calculation yourself, the calculator might have used In not Ib.
Also as sugeted above you can calculate to each light or stage/section and use smaller cable as the load gets lighter along the way.
16.0mm cable?  Are you sure you have done your calculations correctly. 250m spaced 4m apart is 62 or 63 lights (250/4=62.5). 63x8watt lamps is 504watts, 504watts @ 230v is less than 2.5amps. Even if they were all at the end of the 250m if you had 4.0mm @ 11mv/a/m,  (11x2.5x250)/1000 = 6.875.  I thought 6.9v was the acceptable lighting 3% nominal ? But surely you will have 8w @ 250m,  16w @ 246m,  24w @ 242m, 32w @ 238m etc, etc. and only the 500w+ @ 4m along the run.
I point blank refuse to fit stuff to trees,
how are they possibly stable mounting surfaces,? they move every second simply by growing,
The last biggish drive I done, about 100m I put low level coach lamps on little concrete plinths, 2.5mm SWA worked out way more than adequate.