Neff Double Oven 5.7Kw


dave2

Question

Anyone fitted one of these?

 

Do they come with their own supply cable?

 

MI's is for 24A fuse rating but no info to enable me to apply diversity.

 

Had some of these ovens where you can hardly get a 4mm into the connections.

Link to comment
Share on other sites
 

14 answers to this question

Recommended Posts

Manufacturers part number?

Link to comment
Share on other sites
 

Anyone fitted one of these?

 

Do they come with their own supply cable?

 

MI's is for 24A fuse rating but no info to enable me to apply diversity.

 

Had some of these ovens where you can hardly get a 4mm into the connections.

 

so what is the problem?

2.5 will carry 24A,,,,,,,

Link to comment
Share on other sites
 
kerching

Good luck with the 24A fuse!

Link to comment
Share on other sites
 

I'm still looking for a 32a FCU as requested by MI's :innocent

Link to comment
Share on other sites
 
kerching

I rarely struggle to get cables into terminals

I carry a range of crimps from 2x1.0mm double bootlace ferules , through 25to 16 mm pin crimps , 50mm boot lace ferules right up to 400m lugs

Just stopped struggling years ago

Link to comment
Share on other sites
 

Totally different subject but a lot of the main shower manufacturers recommend installing a 45amp MCB.......has anyone found one of them to date?

Link to comment
Share on other sites
 

Totally different subject but a lot of the main shower manufacturers recommend installing a 45amp MCB.......has anyone found one of them to date?

MK do one!

Link to comment
Share on other sites
 
 
 

Model is Neff U15M52N3GB which customer has not yet ordered.

 

Steps--- yes I know 2.5mm will be ok for 24A in most conditions but you can't get 24A mcb's, Next one is 32A which would be to big.

 

So I install 4mm on 32A mcb but MI's state max fuse 24A??????

Link to comment
Share on other sites
 

Model is Neff U15M52N3GB which customer has not yet ordered.

 

Steps--- yes I know 2.5mm will be ok for 24A in most conditions but you can't get 24A mcb's, Next one is 32A which would be to big.

 

So I install 4mm on 32A mcb but MI's state max fuse 24A??????

Hager do 25A MCBs as do Schneider.......

Link to comment
Share on other sites
 

As do most manufacturers 

Link to comment
Share on other sites
 

Got to admit  I didn't think Wylex (existing cu) did 25A mcb's but on checking they do.

 

Thanks for the help.

Link to comment
Share on other sites
 

i think almost all manufacturers do a 25a, just they are not very popular and not normally listed at most places

Link to comment
Share on other sites
 

Archived

This topic is now archived and is closed to further replies.

×