DOES ANYBODY KNOW WHAT TYPE OF BREAKER SHOULD BE USED FOR A THREE PHASE MOTOR,AND WHY,SORRY THIS IS ALL IN CAPITALS,IM NOT SHOUTING,MY KEYBOARD'S BROKE :)
Canoeboy said:
It would really depend on how the motor is starting and what the load type is, so a one size mcb fit all is not really an acceptable answer
The best breaker in my opinion (that i use all the time) for a motor (in general terms) is a motor protective circuit breaker MPCB
http://w3.siemens.com/mcms/industrial-controls/en/protection-equipment/circuit-breakers/pages/default.aspx
The nail that Andy has pointed to was a very old fashioned method that is by todays standards frowned upon......
thank you :)
Have you ever tried to get the max Zs for these?
How often does one of these come under BS7671 though?
Mind, disconnection times due to earth fault loop are relevant under other standards too.
Canoeboy said:
Yes thanks.
You can also ask the manufacturer for the Zs details for the appropriate range of MPCB
Here is a Schneider table, Siemens, ABB and Eaton all have these details although sometimes they are hard to find.
http://www2.schneider-electric.com/resources/sites/SCHNEIDER_ELECTRIC/content/live/FAQS/139000/FA139612/en_US/FA139612.pdf
Thanks for the link
they are hard to find, when I phone to ask, its very hard to find anyone that knows what the Zs means, let-alone what it is