We have all heard and most have seen how NOT to connect PV. I know a few things about PV but here I sit starting to doubt myself. All the PV we have installed to date, we have done a fashion that does not require RCD protection (quite easy to achieve retro-fit). My thoughts, and the regs thoughts, say to use a B Type RCD..... Have you tried to get hold one?

 

Wholsalers....... Nope, never sold them

T'internet......... Struggle to find anyone dealing in them.

 

So, my question for this thread is, how do people fit PV properly when RCD is needed? i,e new build, re-wire, etc.

 

I have seen many installs using garage boards and AC type RCD, to me this is wrong. Wylex seem to offer some PV switchgear and they state that the unit can come with an DP RCBO but nowhere does it say it is a B Type and searching the t'internet return nothing for wylex b type DP rcbo.

 

Now, I have seen some inverter manufacturers state that an A type RCD will suffice as DC can only leak from +ve OR -ve giving the pulsing DC not constant. A lot of RCBO's are A Type, but I wouldn't like to hold this up in court.

 

So, without bashing me sensless with a stick, What configurations have you seen in real life that you deem right?

 

Answers on a postcard (or just reply to the thread)

 

Ta

Share this post


Link to post
Share on other sites
Essex1

Surely the B type you need is for the OPCD and not the RCD.  A B Type RCBO yes but a B type RCD.???

Share this post


Link to post
Share on other sites
Barx

It is a B Type RCD Essex, to deal with DC currents.

Share this post


Link to post
Share on other sites
Rob.
Quote

Residual current devices may also be classified as Type a.c.,Type A and Type B as follows:

 

Type a.c. Ensures tripping for residual a.c. currents, whether suddenly applied or slowly rising.

 

Type A Ensures tripping for residual a.c. currents and pulsating d.c. currents, whether suddenly applied or slowly rising.

 

Type B Ensures tripping for residual a.c. currents, pulsating d.c. currents and smooth d.c. currents, whether suddenly applied or slowly rising.

 

@Essex1

Share this post


Link to post
Share on other sites
Essex1

I knew I should have stayed out of this thread. 

 

This is what happens when you are bored and on a train into London. 

Share this post


Link to post
Share on other sites
Rob.
7 minutes ago, Essex1 said:

I knew I should have stayed out of this thread. 

 

This is what happens when you are bored and on a train into London. 

 

I was just posting the information for reference that's all.

Share this post


Link to post
Share on other sites
Essex1
1 minute ago, Rob. said:

 

I was just posting the information for reference that's all.

 

I know. Scoobed appropriately. 👍👍👍👍

Share this post


Link to post
Share on other sites
Barx
50 minutes ago, Essex1 said:

I knew I should have stayed out of this thread. 

 

This is what happens when you are bored and on a train into London. 

 

10 points for effort though pal :coat

Share this post


Link to post
Share on other sites
binky

that's only about he RCD not tripping all the time as far as I'm concerned. I've always used 'normal' RCDs but not shared with any other circuit. All has been fine to date. The only inverter I have seen that was causing issues with an A type RCd was an Power One unit as mentioned in a previous posting whereby we were advised to ft a 300mA RCD (which did work incidentally), during which we concluded that DC faults can affect the AC side, and I know that array has DC issues with damp. Given the segragation within the inverter of AC and DC, I can't see how DC could ever be present on the AC circuit?

Share this post


Link to post
Share on other sites
Barx

We had 1 install that had an AC RCD in a garage board. It's the only local private install we had done last year and the ONLY install we put an RCD in. No idea why the RCD was there as it wasn't required. Me thinking the lad that did it picked up the wrong garage board type and didn't take notice that it was an RCD (I have checked the others and all okm;)). Just happened to be the install I took MCS inspector to. Got an NC for it not being a B Type. Most TransformerLess inverters are deemed to not have seperation internally. Bloody typical...

 

Changed the RCD to main switch and NC cleared. Inspector reiterated the requirement for B Type when no seperation stated by manufacturer. BTW, this isn't the reason for this thread, inspection was a couple of months ago.

 

I have emailed a few manufacturer's asking if the built in RCD that most inverters seem to have cover faults AC side, none have replied. If it does then the way I see it is when the inverter is live and generating, the inverter RCD protects the circuit even if the Mains side one is locked in place with DC. Then when the inverter is dead, the mains side one works as required still protecting the circuit. There is no concrete evidence of this though and no-one is willing to accept it so all just say 'B Type required'. Like talking to robots.

 

Page one of the following doc shows the reason for needing it

 

http://www.doepke.co.uk/download/Techpub-04.pdf

Share this post


Link to post
Share on other sites
leesparkykent

reg 712.411.3.2.1.2

Share this post


Link to post
Share on other sites
leesparkykent

Does anyone have Februarys professional electrician magazine kicking about? I've chucked my copy but Elecsa have written an article about PV and RCD's IIRC page 37. 

Share this post


Link to post
Share on other sites
Barx

Not seen it Lee, i don't visit wholesalers much these days to pick a copy up. Would be interesting to read that articla though. Can you remember the concensous of it?

Share this post


Link to post
Share on other sites
binky

Interesting article from Doepke. I don't quite see how you get a DC earth leakage. Apart from the fact there is no earth connection on the DC side, the inverters self check as they start up, specifically looking for DC faults. Whether they maintain any form of monitoring after start-up I don't know, although we have earth leakage faults reported during daytime running caused by freak-weather events on SMA units. Given that daylight usually comes in gently, I would have thought a DC leakage would be detected before it reached more than 6mA? I know my Power One often reads 2mA on start up. But I suppose the argument is that on a functioning system, would the RCD do its job? I'm trying to think how the relatively high resistance of an Earth Rod would affect mA leakage, as this is about the only time I would fit an RCD.

Edited by binky

Share this post


Link to post
Share on other sites
Barx

There are loads of articles from others too @binky all saying same thing. Others also mention 'parasitic capacitance'. SMA explain it a bit here -> http://files.sma.de/dl/7418/Ableitstrom-TI-en-25.pdf

 

Here is another interesting point. Wylex do a 'PV Consumer Unit' (bottom of page 4 on this doc -> https://www.tlc-direct.co.uk/Technical/DataSheets/Wylex/WylexSolarPV.pdf) the interesting thing is they do an RCBO version. I have asked Wylex to confirm that the RCBO has B Type RCD parameters...... I just got set a datasheet that does not state the type. Just that the MCB part is 16A 6kA B Curve.

 

 

Share this post


Link to post
Share on other sites
leesparkykent

ok found it.

Requirements of BS7671 connecting the PV a.c. mains.

 

At the connection to the a.c. mains, the PV supply cable must be connected to the supply side (i.e. upstream) of the OCPD's gor the final circuits in the electrical installation (regulation 712.411.3.2.11).

  therefore, the PV supply cable must be a dedicated circuit. It cannot be connected to an existing final circuit of the electrical installation.

When connected in this way, the operation of the protective devices of the other final circuits of the electrical installation is unaffected by the PV installation.

 

Fault protection

 

The PV supply cable on the a.c. side must be protected against fault current by an OCPD installed at the connection to the a.c. mains (regulation 712.434.1). A circuit breaker in a one way consumer unit fulfils this requirement.

 

General requirements

 

The addition of the PV installation must be selected and erected in compliance with the requirements of section 712 of BS7671 and other relevant requirements of BS7671.

 

Earthing & bonding

 

Regulation 712.312.2 states that earthing of one of the live conductors of the d.c. side is permitted, if there is at least simple separation between the a.c. side and the d.c. side. The note to regulation 712.312.2 states "any connections with the earth on the d.c. side should be electricaly connected so as to avoid corrosion (see BS 7361-1:1991)".

A risk assessment should be carried out to determine the presence of any exposed conductive parts or extraneous conductive parts.

where protective bonding conductors are installed, they must be parallel to and in close contact as possible with the d.c. cables and a.c. cables and accessories (regulation 712.54). Where pre-assembled cable harnesses are used, its important to ensure that the cable system complies with the requirements of BS7671.

 

When an RCD is required at the PV inverter end

 

An RCD may be required to provide either fault protection by ADS or additional protection in accordance with regulation 415.1. Where it has been determined that an RCD is required, it must be located at the PV inverter end of the circuit and the type of RCD selected must take the characteristics of the PV inverter in to account.

If the PV inverter, by its construction does not have simple separation between the d.c. side and a.c side ( this is some times called a transformerless inverter), a type B RCD to BS EN 62423 is required as it will detect a.c., pulsating d.c. and steady d.c. currents. Reference should be made to the manufacturer of the PV inverter for advice. Where a PV inverter has simple separation incorporated, the RCD does not have to be type B.

 

When an RCD is not required at the PV end

 

If the purpose of the RCD at the PV inverter end is solely to prove protection against impact, the RCD would not be required if the supply cable was run in a floor or ceiling void, or on the surface or in SWA cable.

Regardless of whether or not the PV inverter has simple separation incorporated, an RCD would not be required in such circumstances.

 

Shared RCDs are not permitted

 

At the a.c. mains end the PV supply cable must not be connected to the outgoing way of a final circuit which shares an RCD with other final circuits (see IET code of practise for grid connected PV systems page 88). The reason this is prohibited is that the other final circuits maybe supplied by the inverter, during the shutting down period. This would mean the required maximum disconnection times for these final circuits could be compromised. In addition, sharing an RCD may cause unwanted nuisance tripping due to accumulation of earth currents.

 

 

 

 

 

Edited by leesparkykent

Share this post


Link to post
Share on other sites
Barx

It is very interesting that they state 'at the inverter end'. I don't remember reading that in any other material I have gone through. What happens to additional protection when the inverter is dead? be it either no generation due to lack of sun or the built in RCD has detected a fault and tripped, this leaving a live AC cable burried in the wall for example with no RCD protection.

 

The mystery contnues...

 

p.s. thanks for digging it out @leesparkykent

Share this post


Link to post
Share on other sites
leesparkykent
3 minutes ago, Barx said:

It is very interesting that they state 'at the inverter end'. I don't remember reading that in any other material I have gone through. What happens to additional protection when the inverter is dead? be it either no generation due to lack of sun or the built in RCD has detected a fault and tripped, this leaving a live AC cable burried in the wall for example with no RCD protection.

 

The mystery contnues...

 

p.s. thanks for digging it out @leesparkykent

No problems. The subject has been  much debated on another forum and after 100 posts it was still as clear as mud lol

Share this post


Link to post
Share on other sites
Canoeboy
10 hours ago, Barx said:

We have all heard and most have seen how NOT to connect PV. I know a few things about PV but here I sit starting to doubt myself. All the PV we have installed to date, we have done a fashion that does not require RCD protection (quite easy to achieve retro-fit). My thoughts, and the regs thoughts, say to use a B Type RCD..... Have you tried to get hold one?

 

Wholsalers....... Nope, never sold them

T'internet......... Struggle to find anyone dealing in them.

 Yes Freely availably from Siemens, Although you wont buy one as they are around £1000 plus VAT, if  you fit decent inverters like SMA then they are tested with both Siemens and ABB standard RCDS and work flawlessly, don't know about other makes.

 

So, my question for this thread is, how do people fit PV properly when RCD is needed? i,e new build, re-wire, etc. Fit SMA and Siemens RCD

 

I have seen many installs using garage boards and AC type RCD, to me this is wrong. Wylex seem to offer some PV switchgear and they state that the unit can come with an DP RCBO but nowhere does it say it is a B Type and searching the t'internet return nothing for wylex b type DP rcbo.

 

Now, I have seen some inverter manufacturers state that an A type RCD will suffice as DC can only leak from +ve OR -ve giving the pulsing DC not constant. A lot of RCBO's are A Type, but I wouldn't like to hold this up in court. SMA are tested for the standard RCDs bit only for ABB and Siemens 

 

So, without bashing me sensless with a stick, What configurations have you seen in real life that you deem right? In real life nothing i have seen locally installed by the muppets has been any good, all would have failed an MCS inspection, Wrong RCD, No RCD, Back Fed DB not at Origin, Panels to edge of roof, Panels overhanging roof apex, Cable Sizes too small, G59 setup as G83, DC Isolators with the links removed..... The list is endless.

 

Answers on a postcard (or just reply to the thread)

 

Ta

 

My Red

10 hours ago, Barx said:

It is a B Type RCD Essex, to deal with DC currents.

 

Correct and Siemens and ABB make them, don't know about the likes of hager and wile but i doubt it.

Share this post


Link to post
Share on other sites
binky

OK, 'at the inverter end' I'll have to double check data sheets but I'm fairly sure decent inverters have this in-built. SMAs have in-built DC string monitoring, so I'm assuming this is effectively RCD protection.

 

Moto:- avoid cheap Chinese inverters

Share this post


Link to post
Share on other sites
binky

from SMA 3600TL data sheet:--

 

Protective devices
DC disconnect device
Ground fault monitoring / grid monitoring
DC reverse polarity protection / AC short-circuit current capability / galvanically isolated
All-pole-sensitive residual-current monitoring unit
Protection class (according to IEC 62103) / overvoltage category (according to IEC 60664-1)

 

I checked a few other makes of inverter, and all have some form of DC moitoring, but are a bit vague with regards to residual current. I would assuem they would monitor for DC leakage to prevent destruction of AC components? So I think answer to quesion is you need to check manufacturers instruction for each make of inverter.

Edited by binky

Share this post


Link to post
Share on other sites
Barx

Just to note there @binky an RCMU is not an RCD.

 

I emailed Afore (another cheap brand) to ask what type of RCD was built into their inverters as in their manual it just says RCD  -  Internal.

 

They replied saying their inverter does not have a built in RCD. LoL

Share this post


Link to post
Share on other sites
binky

indeed it isn't, but the RCd is required against some form of DC leakage, so anything that monitors for said leakage basically performs the same function, probably more effectively....

Share this post


Link to post
Share on other sites
rugbyduffy
On 04/07/2016 at 21:07, leesparkykent said:

ok found it.

Requirements of BS7671 connecting the PV a.c. mains.

 

At the connection to the a.c. mains, the PV supply cable must be connected to the supply side (i.e. upstream) of the OCPD's gor the final circuits in the electrical installation (regulation 712.411.3.2.11).

  therefore, the PV supply cable must be a dedicated circuit. It cannot be connected to an existing final circuit of the electrical installation.

When connected in this way, the operation of the protective devices of the other final circuits of the electrical installation is unaffected by the PV installation.

 

Fault protection

 

The PV supply cable on the a.c. side must be protected against fault current by an OCPD installed at the connection to the a.c. mains (regulation 712.434.1). A circuit breaker in a one way consumer unit fulfils this requirement.

  

When an RCD is not required at the PV end

 

If the purpose of the RCD at the PV inverter end is solely to prove protection against impact, the RCD would not be required if the supply cable was run in a floor or ceiling void, or on the surface or in SWA cable.

Regardless of whether or not the PV inverter has simple separation incorporated, an RCD would not be required in such circumstances.

 

Shared RCDs are not permitted

 

At the a.c. mains end the PV supply cable must not be connected to the outgoing way of a final circuit which shares an RCD with other final circuits (see IET code of practise for grid connected PV systems page 88). The reason this is prohibited is that the other final circuits maybe supplied by the inverter, during the shutting down period. This would mean the required maximum disconnection times for these final circuits could be compromised. In addition, sharing an RCD may cause unwanted nuisance tripping due to accumulation of earth currents. 

 

Good afternoon all,

 

New User here (although I have been an avid reader/spectator a number of years and found the forum a very good source of guidance and advice).

So firstly apologies if reviving this old thread was not the thing to do, but the quote above refers to a number of queries I had around my own PV installation so I thought it the most concise means of asking...

 

I have an SMA Sunnyboy Inverter installed 2012 into an independent circuit of a Dual RCD consumer unit, and whilst we'd always had infrequent nuisance tripping of the 80A RCD protecting that side of the board, the frequency had increased to the point where it became an inconvenience.  (I am aware that PV sharing RCDs is not a good practice from reading these forums, but can only presume that wasn't wide knowledge in 2012 as my New Build home subsequently passed Part P sign-off from my Local Authority).

I had an electrician colleague recently carry out some earth leakage tests on the other circuits which share that RCD in case a cumulative effect was causing it. He found no smoking gun, although he said the results were "not great, but okay". 

 

I carried out a series of investigations where I isolated the PV circuit for weeks at a time and experienced no nuisance tripping whatsoever; with it re-energised I'd typically get a couple a week (between 1-5 times, quite variable in frequency and not definitively linked to weather conditions which I also logged).

 

I recently requested my MCS installer return to my home to investigate as part of the Inverter 10yr warranty and their electricians stated during their visit that they have see a very small proportion of their installs suffer such nuisance tripping, and cited a recommendation that the PV needn't be RCD protected (I'd also expressed my concern after informing myself on this forum of the effect of a secondary supply sharing an RCD with other sockets).

Their course of action was to relocate the circuit to a non-RCD protected side of the board, which whilst having completely eliminated the nuisance tripping problem, has left me with a few queries.

 

1. I'd asked them to provide documentation of this modification for my own records, insurance purposes, etc. They seemed surprised that I'd requested this and stated that they could provide a Minor Works Certificate for me - is this the appropriate documentation for this work? 

2. I have been reading the available extracts of BS7671, in particular "522.6.202 Cables in wall less the 50mm from the surface" which I realise stipulates that I require 30mA protection for this circuit - my solar PV cables are within safe zones in plastic capping under render.   Now that this circuit has been modified am I required to comply with this (presumably more recent) regulation? I say 'presumably more recent reg' as I believe this was a 2015 update, which our home pre-dates (built 2012).

3. Assuming so, is my only option an independent 30mA RCBO for the the single PV circuit, and hope that without any cumulative leakage effects from the "okay, not great" circuits that this will survive my Sunnyboy inverter switching?
4. I have read a lot of manufacturer advice relating to PV nuisance tripping RCD which focuses on uprating to 100mA or 300mA ratings! Am I right to presume that these are applicable only in cases where cables are routed differently to mine, effectively snookering me (as ours were installed in build, not retro-fitted)?

5. Assuming I do need a 30mA RCBO and this suffers similar nuisance tripping, are my only other options to redesign the wiring routes to not require the RCD protection (Regulation 522.6.204 I think stipulates such examples?), or to upgrade our Inverter which is presumably deteriorating somewhat due to the increased frequency of RCD tripping and its 8 year age (I think we were suggested these had a potential life of 10yrs when we purchased the system, although I got the impression the industry was so new that nobody actually knew this as the time we were quoted it).

 

Appreciate a number of queries here, but I would really appreciate the guidance / understanding / experiences of anyone whose come across / overcome similar issues so that I can go back to my MCS Installer with an informed response!

 

Thanks in advance for any support offered.

 

Cheers

Share this post


Link to post
Share on other sites
Murdoch
32 minutes ago, rugbyduffy said:

 

Good afternoon all,

 

New User here (although I have been an avid reader/spectator a number of years and found the forum a very good source of guidance and advice).

So firstly apologies if reviving this old thread was not the thing to do, but the quote above refers to a number of queries I had around my own PV installation so I thought it the most concise means of asking...

 

I have an SMA Sunnyboy Inverter installed 2012 into an independent circuit of a Dual RCD consumer unit, and whilst we'd always had infrequent nuisance tripping of the 80A RCD protecting that side of the board, the frequency had increased to the point where it became an inconvenience.  (I am aware that PV sharing RCDs is not a good practice from reading these forums, but can only presume that wasn't wide knowledge in 2012 as my New Build home subsequently passed Part P sign-off from my Local Authority).

I had an electrician colleague recently carry out some earth leakage tests on the other circuits which share that RCD in case a cumulative effect was causing it. He found no smoking gun, although he said the results were "not great, but okay". 

 

I carried out a series of investigations where I isolated the PV circuit for weeks at a time and experienced no nuisance tripping whatsoever; with it re-energised I'd typically get a couple a week (between 1-5 times, quite variable in frequency and not definitively linked to weather conditions which I also logged).

 

I recently requested my MCS installer return to my home to investigate as part of the Inverter 10yr warranty and their electricians stated during their visit that they have see a very small proportion of their installs suffer such nuisance tripping, and cited a recommendation that the PV needn't be RCD protected (I'd also expressed my concern after informing myself on this forum of the effect of a secondary supply sharing an RCD with other sockets).

Their course of action was to relocate the circuit to a non-RCD protected side of the board, which whilst having completely eliminated the nuisance tripping problem, has left me with a few queries.

 

1. I'd asked them to provide documentation of this modification for my own records, insurance purposes, etc. They seemed surprised that I'd requested this and stated that they could provide a Minor Works Certificate for me - is this the appropriate documentation for this work? 

2. I have been reading the available extracts of BS7671, in particular "522.6.202 Cables in wall less the 50mm from the surface" which I realise stipulates that I require 30mA protection for this circuit - my solar PV cables are within safe zones in plastic capping under render.   Now that this circuit has been modified am I required to comply with this (presumably more recent) regulation? I say 'presumably more recent reg' as I believe this was a 2015 update, which our home pre-dates (built 2012).

3. Assuming so, is my only option an independent 30mA RCBO for the the single PV circuit, and hope that without any cumulative leakage effects from the "okay, not great" circuits that this will survive my Sunnyboy inverter switching?
4. I have read a lot of manufacturer advice relating to PV nuisance tripping RCD which focuses on uprating to 100mA or 300mA ratings! Am I right to presume that these are applicable only in cases where cables are routed differently to mine, effectively snookering me (as ours were installed in build, not retro-fitted)?

5. Assuming I do need a 30mA RCBO and this suffers similar nuisance tripping, are my only other options to redesign the wiring routes to not require the RCD protection (Regulation 522.6.204 I think stipulates such examples?), or to upgrade our Inverter which is presumably deteriorating somewhat due to the increased frequency of RCD tripping and its 8 year age (I think we were suggested these had a potential life of 10yrs when we purchased the system, although I got the impression the industry was so new that nobody actually knew this as the time we were quoted it).

 

Appreciate a number of queries here, but I would really appreciate the guidance / understanding / experiences of anyone whose come across / overcome similar issues so that I can go back to my MCS Installer with an informed response!

 

Thanks in advance for any support offered.

 

Cheers


@binky

Share this post


Link to post
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now

×

Important Information

Terms of UseWe have placed cookies on your device to help make this website better. You can adjust your cookie settings, otherwise we'll assume you're okay to continue.