Wiring replacement pull cord switch


Larches
 Share

Question

I need to replace a pull cord switch for a shower extractor fan, but would appreciate advice regarding wiring as the old and new switches are different types. I'm attaching a picture of each.

The existing switch has common, L1 and L2, with the lives currently going together into COM and both neutrals terminated together - as can be seen in the photo.

The new switch is double pole and has "in" L & N and "out" L & N.

Can anyone confirm the correct config for the new switch please (and what's with the fan 'earth' to L2 on the existing switch)?

Also, there's no hole on the new switch to bring the cables through (as presumably there wasn't on the old one originally either :). There are two oblong recesses that are presumably to be cut out as required, but it's still pretty thick, solid plastic - what's the easiest way of tackling this (without risking knackering anything)?

Thanks!

 

Existing switch.jpg

New switch.jpg

Edited by Larches
Secondary question
Link to comment
Share on other sites

Recommended Posts

  • 0

your fan should be wired in 4 core flex not 3 core using the earth as a live. whoever installed it has bodged it

Edited by Andy™
Link to comment
Share on other sites

  • 0

Or replace the timer fan with a non timer model......... And wire it using the existing 3c with the earth being the earth...

Link to comment
Share on other sites

  • 0

+1 to the above.

 

Assuming it's an upstairs bathroom with access to the loft, it should be easy to replace the 2 core and earth cable with a 3 core and earth cable. Then we can tell you how to wire it. The wiring will be different as your new switch is a double pole switch with a neon "on" indicator lamp.

 

There is a rectangular knock out for cable entry bottom right as shown in the picture.
 

Link to comment
Share on other sites

  • 0
3 hours ago, Andy™ said:

your fan should be wired in 4 core flex not 3 core using the earth as a live. whoever installed it has bodged it

 

No they haven't. Please point me to the regulation which disallows this practice.

 

Yes it would be ideal to wire it in 4 core flex but using 3 core with the G/Y sleeved is not bodging it and there is nothing wrong with what is there.

Link to comment
Share on other sites

  • 0

I'm sure this came up before,

I was always under the understanding that a G/Y marked cable could not be over marked for any use other than an earth/CPC,

But, after the last escapade, I'm unsure if anyone ever came up with a definitive regulation or not, :C

So that's of no help to anyone whatsoever really,,,, :|

 

 

Link to comment
Share on other sites

  • 0
6 minutes ago, steptoe said:

I'm sure this came up before,

I was always under the understanding that a G/Y marked cable could not be over marked for any use other than an earth/CPC,

But, after the last escapade, I'm unsure if anyone ever came up with a definitive regulation or not, :C

 

I'd imagine it has come up a few times. I would concede that this is perhaps "open to interpretation" but using G/Y in a flexible multicore cable is not expressly prohibited.

 

If you are cutting cables mid run on the assumption that G/Y = CPC, Brown = L & Blue = N then you are going to come a cropper before long. If this was the case brown/blue switch drops would be outlawed too.

 

Link to comment
Share on other sites

  • 0

Personally I wouldn't use a Grn/Yell as anything other than a protective conductor.... ref 514.4.2:

protective conductor.jpg

 

I'd also be interested to know if this 230v Fan is in the correct zone in the bathroom?

 

or should it be a 12V?

 

If its a pain in the bum to replace the cable..  long run behind tiles etc...

I'd probably convert it to 12v and stick a transformer and timer close to the switch with a new bit of 3 core + E doing the live & switched lives..

and use the flex to run the 12v to the fan.

 

 

 

Guinness

Link to comment
Share on other sites

  • 0

There is still nothing in those regulations that specifically exclude the use of the G/Y in a multicore cable as a live conductor.

Link to comment
Share on other sites

  • 0

Its a funny one,

Can anyone point out one of the regs that is NOT ambiguous,?

An internet Pint for the winner, Guinness

5 minutes ago, Lurch said:

There is still nothing in those regulations that specifically exclude the use of the G/Y in a multicore cable as a live conductor.

I'd agree, 

With that reg it would appear to be merely a 'good practice' thing, and, if needs must,,,,        

Link to comment
Share on other sites

  • 0
6 minutes ago, Lurch said:

There is still nothing in those regulations that specifically exclude the use of the G/Y in a multicore cable as a live conductor.

 

There is nothing that says it is an acceptable use.....

 

16 minutes ago, Lurch said:

 

. If this was the case brown/blue switch drops would be outlawed too.

 

 

Brown & Blue switch drops ..  (sleeved brown)

and two switching with Brown / Black / Grey    (also sleeved brown)

 

Are specifically mentioned in Appendix 7 top of page 436.... as being acceptable

 

But...  I can't see any mention stating that grn/yel over-sleeved brown is an acceptable practice anywhere????

 

We do also have the Reg; 412.2.3.2  (pg 66) that requires a CPC to be run to each point and accessory in a circuit supplying one or more items of Class II equipment.

So strictly speaking a CPC would still need to be run to this fan to comply with BS7671.

 

:popcorn

Link to comment
Share on other sites

  • 0
7 hours ago, Lurch said:

There is still nothing in those regulations that specifically exclude the use of the G/Y in a multicore cable as a live conductor.

 

correct, but an earth should be taken to every point. so its still wired wrong

Edited by Andy™
Link to comment
Share on other sites

  • 0
42 minutes ago, Andy™ said:

but an earth should be taken to every point. so its still wired wrong

 

I could probably class that as the appliance cord, and as such it doesn't need an earth if the appliance is class 2. Again, the ambiguity of the regs would make it hard to argue that as being incorrect, specifically.

Link to comment
Share on other sites

  • 0

Anybody want to email the Technical Helpline at NICEIC?

 

i feel,that I personally will not get an answer :innocent

 

like others I am sure I have seen somewhere that it is acceptable, prob in a magazine

 

but I cannot remember where or when

Link to comment
Share on other sites

  • 0
9 hours ago, Lurch said:

 If this was the case brown/blue switch drops would be outlawed too.

 

Actually, in ireland brown/blue switch drops are outlawed. We use twin brown.

 

I can't remember the reg @Risteard will be able to quote it.

Link to comment
Share on other sites

  • 0

I remember never being allowed to use red/black in norn iron, always had to be twin red, and nihe specified big earth 1.5, ie, a 1.5 with a 1.5 earth. 

Link to comment
Share on other sites

  • 0

I feel a little sorry for the original poster who must be quite bewildered by the discussion he has triggered.  What he has there may be incorrect to regs but in my opinion isn't actually unsafe. May I suggest that the following is helpful.

 

Lin  =  Red + Brown 

Nin =  Black

Lout = The sleeved green core of the flex

Nout = Blue

 

 Terminate the incoming (unused) earth core in the terminal provided in the new box, just as it was in the old.

As regards opening up the knockouts, if they are tough to pierce start with a small drill and open up with a file. As  space appears tight in the new switch it will probably be best to separate the incoming and outgoing cables and use both knockouts. Shorten the wires to lay neatly, with the cable sheaths finishing just inside the box. (i.e. do not just push spare wire back up into the void.)

Link to comment
Share on other sites

  • 0
11 hours ago, SPECIAL LOCATION said:

Personally I wouldn't use a Grn/Yell as anything other than a protective conductor.... ref 514.4.2:

protective conductor.jpg

 

I'd also be interested to know if this 230v Fan is in the correct zone in the bathroom?

 

or should it be a 12V?

 

And what zone would that be ?

As long as the fan is ip4x(which most are) and RCD protected why waste money on a 12v fan

 

 

 

Guinness

 

Link to comment
Share on other sites

  • 0
1 hour ago, Geoff1946 said:

 

Lin  =  Red + Brown 

Nin =  Black

Lout = The sleeved green core of the flex

Nout = Blue

 

 

er... if it fan has a timer (which i would assume for how its been wired) then that wiring method will stop the timer function from working...

 

L in brown & red

L out g/y sleeved brown

N in black & blue

 

a bit like a job a long time ago where the architect insisted on DP switching for the lights and refused to listen to why it should be SP, then finally agree'd to SP after the job was complete and pointed out that the emergency lights come on every time you turn the light switch off...

Edited by Andy™
Link to comment
Share on other sites

  • 0
11 hours ago, Lurch said:

There is still nothing in those regulations that specifically exclude the use of the G/Y in a multicore cable as a live conductor.

 

11 hours ago, steptoe said:

Its a funny one,

Can anyone point out one of the regs that is NOT ambiguous,?

An internet Pint for the winner, Guinness

I'd agree, 

With that reg it would appear to be merely a 'good practice' thing, and, if needs must,,,,        

Hang on, I'm lost here, theres a reg there that states "Green+yellow shall be used exclusively for identification of a protective conductor, and this combination shall not be used for any other purpose." Next bit says it shall not be oversleeved at its terminations.

 

So whoever has wired that switch/fan has used green/yellow as a live conductor, and oversleeved it, yet you say theres nothing in the regs to say not to do so?

I'm not seeing your logic.

Link to comment
Share on other sites

  • 0
45 minutes ago, Andy™ said:

 

er... if it fan has a timer (which i would assume for how its been wired) then that wiring method will stop the timer function from working...

 

L in brown & red

L out g/y sleeved brown

N in black & blue

 

a bit like a job a long time ago where the architect insisted on DP switching for the lights and refused to listen to why it should be SP, then finally agree'd to SP after the job was complete and pointed out that the emergency lights come on every time you turn the light switch off...

Shoot!  Your absolutely right. I put the neutrals on the switch so the neon would work, but neutral is needed all the time!  Apologies 

Edited by Geoff1946
Link to comment
Share on other sites

  • 0
2 hours ago, sprocketflup said:

 

Hang on, I'm lost here, theres a reg there that states "Green+yellow shall be used exclusively for identification of a protective conductor, and this combination shall not be used for any other purpose." Next bit says it shall not be oversleeved at its terminations.

 

So whoever has wired that switch/fan has used green/yellow as a live conductor, and oversleeved it, yet you say theres nothing in the regs to say not to do so?

I'm not seeing your logic.

It says 

Single core cables 

We're using a multi core here,

 

Ambiguous,? :C

 

Link to comment
Share on other sites

  • 0
4 hours ago, Geoff1946 said:

I feel a little sorry for the original poster who must be quite bewildered by the discussion he has triggered.  What he has there may be incorrect to regs but in my opinion isn't actually unsafe. 

 

I take issue with that. Using the CPC as the switched live IS unsafe, it is an un  insulated cable with just the sheath to protect it.


 

It would be a bit less unsafe, if the CPC had been used as a substitute neutral, brown for permanent L and blue for switched L.


 

the fact that it's a brown / blue to the fan suggests it's a recent cable and also implies it is quite likely that it won't be to hard to replace it with a 3 core & E to do the job properly.

 

Edited by ProDave
Link to comment
Share on other sites

  • 0
6 minutes ago, ProDave said:

I take issue with that. Using the CPC as the switched live IS unsafe, it is an un  insulated cable with just the sheath to protect it.


 

It would be a bit less unsafe, if the CPC had been used as a substitute neutral, brown for permanent L and blue for switched L.


 

the fact that it's a brown / blue to the fan suggests it's a recent cable and also implies it is quite likely that it won't be to hard to replace it with a 3 core & E to do the job properly.

 

 

if it was T&E, then yes. but its flex. the insulation is the same as the L&N

Link to comment
Share on other sites

  • 0
3 hours ago, Adrian said:

And what zone would that be ?

As long as the fan is ip4x(which most are) and RCD protected why waste money on a 12v fan

 

I would imagine you would call it Zone1 ???:C

 

701.55 specifically states that equipment should be suitable for Zone 1 ref the manufactures instructions  (pg 208 bottom quarter)

 

Take a typical 230v IP44 bathroom extractor fan such as http://www.screwfix.com/p/manrose-mg100t-20w-gold-standard-axial-bathroom-extractor-fan-w-timer/62530#product_additional_details_container

Ceiling or wall mounted item...

 

The instructions http://www.free-instruction-manuals.com/pdf/pa_474957.pdf   specifically say:-

fan instructions.JPG

 

Which to me doesn't say bang it anywhere with an RCD as its IP44...

and as Zone1 is the vertical bit up above the bath or shower that's the Zone where is shouldn't be at a guess?

 

So as I said earlier it is possible that the OP's fan is not suitable for its installed location anyway! 

Agreed NOT ALL manufactures fans may have the same installation instructions... But I have seen enough over the years that do, hence my earlier comment..

 

And at the end of the day when giving advice to DIY'ers on an open public forum I would tend to be cautious about what we who are supposedly the knowledgeable ones,

say can and can't be done in a safe and/or compliant manner with ref to current regs.

 

If IP4x was all that was needed I doubt manufacturers would bother making 12v fans either!

 

:popcorn 

 

 

Link to comment
Share on other sites

  • 0
1 hour ago, Andy™ said:



 

if it was T&E, then yes. but its flex. the insulation is the same as the L&N

I must admit, from the original picture I thought it was t&e with a green / yellow sleeve on the CPC and then a brown sleeve over.


 

I should have gone to (insert name of your preferred optician)

 

I still maintain, if you are going to use green / yellow as anything other than a CPC, then using it as the neutral would be less dangerous.

 

Edited by ProDave
Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Answer this question...

×   Pasted as rich text.   Restore formatting

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

 Share



FORUM SPONSORS


Test Equipment Manufacturers
Electrical & Tool Suppliers
Tool Manufacturers
Electrical Software
Education & Training
To Advertise and become a Forum Sponsor of

talk.electricianforum.co.uk, please

contact the Administrator

Here Thank You.




×
×
  • Create New...

Important Information

Terms of UseWe have placed cookies on your device to help make this website better. You can adjust your cookie settings, otherwise we'll assume you're okay to continue.