Abit confused, need help with sunbed

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

vad25

Member
Joined
Jul 6, 2009
Messages
60
Reaction score
0
Hello every one.

I hope somebody can help me, so as I'm a bit confused about technical data received from client to provide new circuit for sunbed.

 It is made in America and 3ph but 230 volts and I can't see Neutral incoming.

Also some instruction from contractor guides:

This unit requires a 230 volts, three phase, 80 amp (4 wire) circuit

actual amp draw of 58 amps

This unit has approximately 5 ft. of # 4 AWG wire (3 hots, 1

ground) coming out of the left side of the back panel

Will be it correct if I install 63 Amp MCB and rotary isolator with same rating or it must be 80 Amp.

Thank you

sunbed 001.jpg

 
This is NOT suitable for the UK, wrong voltage. Tell the client to send it back and buy one that is rated for the UK  I will bet it does not have a CE mark

Even if it was, at 21KVA you would not get me under it, you would be burnt to a crisp in no time.

 
Last edited by a moderator:
Following to your advice I'm already inform client and she agreed.

 
Thank you to all of you for reply.

After client contacted with sunbed supplier it been confirmed that it is 400 volts 50 amps. and my job is just provide circuit and isolator.

Thank you again

 
Thank you to all of you for reply.

After client contacted with sunbed supplier it been confirmed that it is 400 volts 50 amps. and my job is just provide circuit and isolator.

Thank you again


Is it CE marked, or are the supplier and the user both willing to break the law of the land?

 