ProDave

Attached should be the instructions for a machine I have to insttall

 

A few snippets

 

Voltage 220V

Earth leakage 50mA

Basic power requirement 800W

Fuse  16A delayed action surge proof

Permanent 10mm ground cable

Connected directly to distribution board.

 

The plan was a 16A radial circuit in 2.5mm from the (non RCD) distribution board to a rotary isolator and the machine hard wired into that.

 

But 10mm earth as well as my 2.5 supply? Bonkers. I can't see a 10mm earth fitting the earth terminal in most rotary isolators unless I go up to 63A

 

Looks like a load of hogwash written by someone that knows nothing about electrics.

 

I wonder if it comes with a CE mark?

SitePreparationManual_sciFLEXARRAYER SX.pdf

Edited by ProDave

Share this post


Link to post
Share on other sites
Phoenix

I'd imagine the 10mm is do to the high earth leakage, its either that or 2 earth paths.

 

I think I'd put the 2.5 supply in rom the board to the isolator as you describe, and also put a 10mm in separatly straight to the machine from the board not going through the isolator to keep the commisioing enginner happy, although as you have now got 2 earthss, in BS7671 terms it doesn't have to be as big a 10mmm

Share this post


Link to post
Share on other sites
Sidewinder

The requirement is from the drives used in the machine, you may get leakage spikes of significant magnitude.

 

 Looking at the link I would say that the unit is probably not far off compliance.

 

 I would steer clear PD & leave the PUWER reg 10 due diligence to the user.

 

Mind, I am in Cardiff airport departures waiting for the Edinburgh flight at the moment to look at 2 machines tomorrow in Leven!

So it’s not a problem if they want somebody to discharge their duties to.

 

Depending how far North, between £2 & £3k plus expenses would be in the ballpark.

Share this post


Link to post
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now

Sign in to follow this  


FORUM SPONSORS


Electrical Test Equipment
Test Meter Calibration
Test Equipment Manufacturers
Electrical & Tool Suppliers
Tool Manufacturers
Electrical Software
Green & Renewables
Label Supplies
Accounting Software
Education & Training
Motoring


To Advertise and become a Forum Sponsor of

talk.electricianforum.co.uk, please

contact the Administrator

Here Thank You.




×