strange one

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

revjames

'funny' man™
Supporting Member
Joined
Aug 22, 2009
Messages
4,517
Reaction score
88
Location
Anglesey North Wales
Guy at work (a fitter) told us his lights were going dim at home and TVs dropping out etc. We lent him a MFT and told him to plug it in and observe the voltage. He took photos of the display, which at one point was indicating 135v! 

Heres the strange thing. When the voltage is low, if he switches a kettle or cooker on, the voltage instantly goes up to 245v. He even videoed the display and you could see the voltage going up when he put the kettle on. The only thing I could think of was some kind of voltage regulator on the DNO side which ups the voltage when a load is detected. But really, 135v?

 
I am thinking if you imagine a circuit.......

Suppliers Live to one side of an open circuit load [call this "A"].

Other side of open circuit load to one side of a high resistance neutral joint [call it "B"]

Other side of a high resistance joint direct back to suppliers neutral [Call this "C"]

When reading the low voltage between A & B you have a high resistance back to the Neutral via B & C.....

If you read A to C you would have full voltage.

With no load connected, If you read between B and C you would have negligible voltage as the load is open circuit.

But if we stick a low resistance (high power) load across A & B,... 

the potential between B & C will rise because the load is now a low resistance bring B nearer to the suppliers live potential..

As the potential rises it will eventually breach the high resistance gap and break down the poor N connection.....

While the resistance between B & C is lowered the voltage at A & B will increase back to the suppliers potential.

Or at least that's what my Friday night head tells me.....  Guinness Guinness Guinness Guinness Guinness

 
I would want to see that volt meter on the input terminals of the CU before making any diagnosis.

It clearly needs fixing, so he needs an electrician.

 
what are you trying to say? the ex office worker who's had 1 day basic trainign in electrics might not have tightened the screw properly or wired it wrong?

 
On a there phase area supply with a failed neutral somewhere near the transformer weird things happen to the Ph → N voltage but totally opposite to what’s happening here. Testing Ph → E and N → E voltage would help as it will point to which side of the supply is acting strangely.

Are his neighbours having problems?

Whatever it is the DNO will have to be involved.

 
Last edited by a moderator:
havent visited the property as he lives in the sticks but am assured all connections are tight

What voltage is he measuring?? Phase/neutral or phase/earth??

Earthing type???

john..
not sure of earthing type but its an overhead supply so could be TNCS he is measuring voltage by plugging MFT into a nearby socket

 

Latest posts

Top