Just want to check when a commando socket is rated at 63A, (4 pins and earth) that's 63A total, not per phase. I've read a few data sheets and this point isn't clear.

 
Just wanted to check Rob, I don't do much 3 phase work, so I'm a bit rusty in this area. I've got a customer who tells me he needs a 20kW supply, but somehow has got in his head he wants a 63A socket on a 63A MCB and cables to suite 63A per phase. (I think he is confused) Now 20 kW is roughly 80Amps, cable run is 45m clipped direct to wall. Now rough calculations would suggest a 6mm cable would suffice for the load. I am planning to install 10mm, table 4E2A says 71A (total) for 4 core. THe load is to charge batteries, so I'm working on the basis the load will be quite steady for quite some time and larger cable cost will be outweighed by reduced energy loss and wasted leccy. Now if what he really wants is 20kW per phase, that's a bit of a larger cable  :^O

Thar's a big un. What's going to plug into it?
batterys

 
Last edited by a moderator:
I make out that 20kW load to be around 32amp a phase based on 400V. Although I don't know what the pf of the load is. 

10mm will be ample, dependent on your Zs requirement. 

 
OK, customer reports that it is 23kW total load, so I make that about 42Amps total or 16A per phase, so we would be happy on a 20A MCB and a 20A commando socket with a 10mm 4 core XLPE SWA rated at 73A, 6mm is rated at 53A according to the big yellow book, so a l ittle undersized  though it would probably work fine!

 
do they do a 20A commando socket?

I have only see 16A,32A,63A,125A ones after that its 200A,250A,and so on but there not commando

 
Last edited by a moderator:
OK, customer reports that it is 23kW total load, so I make that about 42Amps total or 16A per phase, so we would be happy on a 20A MCB and a 20A commando socket with a 10mm 4 core XLPE SWA rated at 73A, 6mm is rated at 53A according to the big yellow book, so a l ittle undersized  though it would probably work fine!


23kW @400V I get 33.2A per Phase.

 
That gives amps per phase. The route 3 take care of that. 

W / (√3 * PF * V*eff)

Efficiency can be taken as 1 if the load is purely resistive, i.e not a motor. 

23000 / (√3 * 0.95 * 400 * 1)

 
Last edited by a moderator:
Ok pinched the figure from Doncaster cables 23kW / 41.5A 6mm cables in XLPE.

so tables at back of big yellow book give amps per phase for 3/4 core cables or amps total?

 
Ok pinched the figure from Doncaster cables 23kW / 41.5A 6mm cables in XLPE.

so tables at back of big yellow book give amps per phase for 3/4 core cables or amps total?
That’s amps per phase. Also which table are you looking at? 70 or 90c cables?

you should be using 70c cable unless the terminations can take 90c

 
Thought so but mislead by a post on another forum.

planning on using 90c cables - smaller. Not heard of any restrictions from terminations before.
You should be using 70c cable. 90c has a higher operating temp hence the requirement for terminations within accessories being able to withstand the higher temps. 

If you look at the 90c table in the BYB there’s a caveat about temps. 

 