M Mikey1959 New member Joined Oct 3, 2018 Messages 2 Reaction score 0 Oct 3, 2018 #1 Does anybody know the formula to the question or the page to go to The maximum measured ZS for BS3036 30A type fuse supplying a cooker circuit not incorporating socket outlet and on a TN system
Does anybody know the formula to the question or the page to go to The maximum measured ZS for BS3036 30A type fuse supplying a cooker circuit not incorporating socket outlet and on a TN system
Sidney Well-known member Joined Feb 24, 2018 Messages 456 Reaction score 87 Location St Neots Oct 3, 2018 #2 Table 41.2 (0.4 seconds) in the new book page 61 or table 41.4 (5 seconds) on page 63. See 41.1 on page 59 for maximum disconnection times for earthing arrangements. Last edited by a moderator: Oct 3, 2018
Table 41.2 (0.4 seconds) in the new book page 61 or table 41.4 (5 seconds) on page 63. See 41.1 on page 59 for maximum disconnection times for earthing arrangements.
M Mikey1959 New member Joined Oct 3, 2018 Messages 2 Reaction score 0 Oct 4, 2018 #3 Sidney said: Table 41.2 (0.4 seconds) in the new book page 61 or table 41.4 (5 seconds) on page 63. See 41.1 on page 59 for maximum disconnection times for earthing arrangements. Click to expand... Thanks Sidney