Question

PaulieN

New here so hello everyone.

 

I have a stupid question for you all. Would like to know the answer from a safety point of view as well as current compliance point of view. I am a qualified electrician but left the profession way back in 1994 for a more lucrative profession, so rusty to say the least.

 

The garage of my new house has a 2.5mm T&E radial circuit feeding half a dozen double sockets. Fine with this as it's just at 50m2, so OK there and the number of sockets is for convenience, load won't be over the 20A, so all good so far. Along side one of the sockets is a 16A commando. This is wired into the radial along with the 13A's.

 

I can't find a reason why this isn't OK, but likewise can find no guidance to say it is either. In an ideal world I'd have it on it's own 16A circuit, but the regs state 16A's are OK on multiple socket 20A protected circuits but don't seem to specify a limitation to the type of sockets. The job is beautifully done in plastic conduit to eaves height everywhere and then the neatest clipping you've ever seen along the rafters to a 2 gang CU with the 20A radial and a 6A lighting circuit. Changing the CU to something wider isn't desirable as it fits perfectly in a recess behind the doors.

Any thoughts?

 

Share this post


Link to post
Share on other sites

22 answers to this question

Recommended Posts

  • 0
ProDave

Change the 20A mcb to 25A  to get the most from that radial circuit.

 

Or it it's never tripping, leave it as it is.

Share this post


Link to post
Share on other sites
  • 0
PaulieN

Thanks for the quick feedback! Can't though, the SWA feeding the garage is only 2.5mm and the length of run is borderline for voltage drop with a 20A, so I'm stuck with it, as I'm not digging up 25M of block paving and concrete to upgrade it. lol!! It's protected at the main CU in the house with a 25A MCB due to this. The garage lighting load with everything on is 3.6A, so I'm way out of spec if I upped it to 25A. 

 

I'm OK with 20A, and disciplined enough to minimise other use if I'm using my welder in the 16A socket. It's just niggling at the back of my head that it's not compliant.... just would like a definitive as to why not if it isn't I suppose. Was done in around 2013 I think, so might be OK for the time, but not now due to current part P nonsense? 

Share this post


Link to post
Share on other sites
  • 0
Sharpend

Part p came about in 2004/5 so not an issue there. 

I wonder if this commando was put in by specific request perhaps for a caravan? 

Share this post


Link to post
Share on other sites
  • 0
Andy™

553.1.201 may apply

 

Quote

Every socket-outlet for household and similar use shall be of the shuttered type and, for an a.c.
installation, shall preferably be of a type complying with BS 1363.

 

 

Share this post


Link to post
Share on other sites
  • 0
Evans Electric

Does your welder work from a 13A socket ?   Or do you need the 16A Commando  for it?

 

Have to say , if it doesn't trip , leave it alone  it sounds safe enough other than no mention of  RCD .

May be some VD  but as you say ...you're not going to dig up the patio. 

Edited by Evans Electric

Share this post


Link to post
Share on other sites
  • 0
binky

I really don't understand what you think the problem is? A twin socket could have 2off 13A appliances plugged in.

Share this post


Link to post
Share on other sites
  • 0
PaulieN

Thanks for the replies. Not really worried about it, just curious if it is to regs. Never come across it before. Of course definitely wouldn't comply if on a 32A ring, but as the circuit is a 20A radial it sits OK with regs for protection at least. Shutter may be a good point. I wonder if it's still classed as household use though as it's a seperate garage? Doesn't worry me at all as there's no access to children and, yes it's all covered by a 30mA RCD. 

 

Previous owner did have a caravan and the socket is nearest to the door, so probably was used for a hook up thinking about it.

 

The welder does need 16a, it pops 13a fuses when it feels in the mood! 

Share this post


Link to post
Share on other sites
  • 0
Andy™

thats the thing, 7671 doesnt define household use. so imo in a garage isnt 'household use'

 

worst case, you can get interlocked versions so you cant turn on the power unless there is a plug inserted which would comply. many welders do tend to pop 13a fuses too, although inverter ones on a lower setting are usually OK

Share this post


Link to post
Share on other sites
  • 0
Adrian

So you over current protection for that 16amp socket is the 20 MCB that can't be right 

Share this post


Link to post
Share on other sites
  • 0
Andy™
2 minutes ago, Adrian said:

So you over current protection for that 16amp socket is the 20 MCB that can't be right 

 

OSG says otherwise. allows a 16a on a 20a OCPD

Share this post


Link to post
Share on other sites
  • 0
PaulieN

Regs say (unless 18th edition has altered this!) 1, 16A on a radial circuit should be a protected at 16A,, multiple 16A can be on a radial protected at 20A, so that's OK, just no specifics on mixing socket types, but doesn't state you can't!

Edited by PaulieN

Share this post


Link to post
Share on other sites
  • 0
Adrian

Seems they need to redefine the socket and call it 20 amps. or better still say each outlet must have 16 amp ocpd provided at evey point 

Share this post


Link to post
Share on other sites
  • 0
Murdoch
12 hours ago, binky said:

I really don't understand what you think the problem is? A twin socket could have 2 off 13A appliances plugged in.

 

and not last very long!

10 hours ago, Adrian said:

Seems they need to redefine the socket and call it 20 amps. or better still say each outlet must have 16 amp ocpd provided at evey point 

 

Ah the delights of BS 7671 - written by people who never get their hands dirty, so have no idea how poorly they are worded, or interpreted....

I would say that the 16A commando should be protected by a 16A MCB...........probably a type C

Share this post


Link to post
Share on other sites
  • 0
kerching

The regs are an ass in places

 

16A commando on 20A breaker....wrong

2 x 16A commandos next to each other BUT you will only EVER use one of them because you only have ONE welder and have no intention of buying anything else....complies

 

 

just saying

Share this post


Link to post
Share on other sites
  • 0
PaulieN

Yep, It's crazy. I've decided it's staying exactly as it is now lol!!

Share this post


Link to post
Share on other sites
  • 0
Adrian
On 08/10/2018 at 18:51, binky said:

I really don't understand what you think the problem is? A twin socket could have 2off 13A appliances plugged in.

Your plug has a 13 amp fuse fitted for protection the 16 amp commando socket has none 

Share this post


Link to post
Share on other sites
  • 0
Tony S

BS1363 only calls for 13A in one outlet and 10A in the other. Total, 23A.

Share this post


Link to post
Share on other sites
  • 0
PaulieN
5 hours ago, Tony S said:

BS1363 only calls for 13A in one outlet and 10A in the other. Total, 23A.

 

Which is a ridiculous and non enforceable regulation as joe public will happily plug in 2, 13A appliances, blissfully ignorant of this restriction!

Share this post


Link to post
Share on other sites
  • 0
kerching

I think sockets have 20A max stamped on the rear WHICH EVERYONE SEES :slap

Share this post


Link to post
Share on other sites
  • 0
Sharpend
9 hours ago, kerching said:

I think sockets have 20A max stamped on the rear WHICH EVERYONE SEES :slap

 

Am I the only one who writes this on the front of the socket????

Share this post


Link to post
Share on other sites
  • 0
Murdoch
2 hours ago, Sharpend said:

 

Am I the only one who writes this on the front of the socket????

 

Why?

Share this post


Link to post
Share on other sites
  • 0
binky
On 08/10/2018 at 20:35, Adrian said:

So you over current protection for that 16amp socket is the 20 MCB that can't be right 

 

but what comes with  16A commando socket fitted?

 

Now I have seen overloaded 16A commando socket, used to supply a burger van, but that is bad design of the van, and whoever built it should have allowed for the electrical demand being higher than the socket could cope with. Even then this particular installation only burns out the commando socket about once every 4 years.

Share this post


Link to post
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now

×

Important Information

Terms of UseWe have placed cookies on your device to help make this website better. You can adjust your cookie settings, otherwise we'll assume you're okay to continue.