Circuit protective conductor

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

Oras

New member
Joined
Oct 28, 2018
Messages
2
Reaction score
0
When installing a sub main swa with a separate Cpc to a distribution board should the Cpc go directly to the main earth terminal and not to the banjo on the gland then up to the m e t 

 
Is that in the regs to do that 


If you have actually read any of BS7671 you should understand it is not an installation instruction book, you will not find wire X must go to terminal Y then Z. As with far to many instances multiple solutions can all meet the wiring regulations requirements.  The regs would be too big to carry if it had to describe every permissible connection method to every conductor in all types of enclosures etc. It is the skill, knowledge and expertise of the person doing the work who will assess if their installation meets BS7671, and sign the appropriate certificate to say their work is compliant.