Bonding ..again !

Recommended Posts

Evans Electric

Just reading in the   NICEIC Connections magazine    Q &A s   

Summed up , no need to bond pipework  that enters the building   insulated  then changes to  copper .  Thats what they say .

 

To old Pharts like me  ...THAT  WAS ONE OF  THE REASONS  WE BONDED IT ....    to allow the mains to be PME   ALL metallics  had to be bonded  .

 

With this NOT bonding it  I imagine a  faulty cable  under the floor,   exposed live  touching the pipework ,  the pipework is stand alone  without Earth  potential so becomes live .

MCB does not operate because its not a short ....RCD does not operate ..UNTIL ...a person makes a  circuit between live & earth .    

That not good surely ?     RCDs are NOT tested  at the recomended times     

Share this post


Link to post
Share on other sites
Sidney

The caveat of testing to see if extraneous seems to be missing.

 

The pipework would normally be directly or indirectly connected at the boiler manifold and in turn the CPC of the boiler supply circuit ergo it wouldn't need bonding as connection could be confirmed by testing.

 

However is that 1.5mm CPC suitable for use as a bonding conductor?

Share this post


Link to post
Share on other sites
ProDave

Lets go back to the old practice of a little earth clip on the bottom of each radiator and an earth wire to each radiator.

 

And who was it had to bond a metal door stop screwed to the ground once?

 

And an earth on the metal tag provided on a steel or cast iron bath, and stainless steel kitchen sink.

Share this post


Link to post
Share on other sites
Sidewinder
2 hours ago, Evans Electric said:

...

 

With this NOT bonding it  I imagine a  faulty cable  under the floor,   exposed live  touching the pipework ,  the pipework is stand alone  without Earth  potential so becomes live .

MCB does not operate because its not a short ....RCD does not operate ..UNTIL ...a person makes a  circuit between live & earth .    

...

 

This scenario requires earthing, not bonding.

Cables are supposed to be adequately separated from mechanical services

Conductors need adequate mechanical protection.

 

How did this cable become damaged in any case, and get into contact with the pipework?

Share this post


Link to post
Share on other sites
Evans Electric
3 hours ago, Sidewinder said:

How did this cable become damaged in any case, and get into contact with the pipework?

I've seen it quite a few times ,  plumber shoves his pipe under the floor ...damages a cable ..  or rodent chews the PVC off  .... bare conductor is touching the free standing pipe   .   Or he does some soldering & melts the cables . 

6 hours ago, Sidney said:

The pipework would normally be directly or indirectly connected at the boiler manifold and in turn the CPC of the boiler supply circuit ergo it wouldn't need bonding as connection could be confirmed by testing.

There is no boiler  ..say . 

 

You may have noticed that I find in difficult to make the transition from  being told we MUST bond ALL  metal pipework  with 6mm  G/Y   ,  Gas & water ,  sinktops MUST be bonded .    If this is not carried out  the Electricity Board  will refuse to connect the  installation .   You have to create a  Faraday Cage  because  a phase reversal on the  PME supply  could have disastrous results. 

 

Followed by , Oooops we dropped a clanger ,  all bonding is now 10mm  .

 

And today ....Oh don't bother , the RCDs will cover everything . 

 

Just being Devil's Advocate here. 

Share this post


Link to post
Share on other sites
Sidewinder
47 minutes ago, Evans Electric said:

Just being Devil's Advocate here. 

 

So am I! ;)

 

So, we have to now allow for others to maliciously damage wiring by their incompetence and not do anything about it?

 

I get where you are coming from, I think, but, there is more to it than that.

 

The idea of bonding is not to detect a fault.

 

Bonding is to limit the touch potential in the event of a fault, it is to keep any metalwork that could be an extraneous-conductive-part at the same potential throughout the equipotential zone in the event of a fault.

It is the job of earthing to limit the duration of the fault.

 

Share this post


Link to post
Share on other sites
Evans Electric

So  ... if the water pipes were bonded ( in 10mm )   to the MET  as they call it  , this fault would have tripped an MCB as a dead short  ...and not just sat there  with 240V on it  , waiting for someone to jump in the bath perhaps. ?  

But as they are saying  not to bond or earth  floating metalwork  ....I just don't get the change in thinking ,  The Faraday Cage chucked  'art the winda .  

Share this post


Link to post
Share on other sites
phil d
5 hours ago, ProDave said:

Lets go back to the old practice of a little earth clip on the bottom of each radiator and an earth wire to each radiator.

 

And who was it had to bond a metal door stop screwed to the ground once?

 

And an earth on the metal tag provided on a steel or cast iron bath, and stainless steel kitchen sink.

You forgot about aluminium window frames, oh wait, didn't that end with a dead window cleaner?

Share this post


Link to post
Share on other sites
ProDave

Have you ever been in a house with a failed PEN on the PME supply?

 

I have once, It was really weird, nothing seemed to be live, yet everything must have floated up to pretty much L potential. The Faraday cage effect.  That was in an old house with all solid copper pipe and earth bonding in place.

 

Now how would that have been if the in coming water main had a plastic section and so was deemed not to be extraneous and not need bonding?

 

Would YOU be happy that the pipework could now end up at a different potential to everything else?  Say the unbonded copper pipe was sitting in a puddle under the floor?

 

Share this post


Link to post
Share on other sites
steptoe
5 minutes ago, ProDave said:

Have you ever been in a house with a failed PEN on the PME supply?

 

I have once, It was really weird, nothing seemed to be live, yet everything must have floated up to pretty much L potential. The Faraday cage effect.  That was in an old house with all solid copper pipe and earth bonding in place.

 

Now how would that have been if the in coming water main had a plastic section and so was deemed not to be extraneous and not need bonding?

 

Would YOU be happy that the pipework could now end up at a different potential to everything else?  Say the unbonded copper pipe was sitting in a puddle under the floor?

 

 

I got called to a job once that turned out to be reverse polarity on a TNCS

they had pulled the fuse to do something and couldnt understand how the 'workman' still got a shock

DNO were out within an hour of me phoning them

that was a scary situation, NO overcurrent protection whatsoever for the installation

 

what would earthed pipes have done in that situation.?  DISCUSS

 

Share this post


Link to post
Share on other sites
Sidewinder
41 minutes ago, ProDave said:

...Say the unbonded copper pipe was sitting in a puddle under the floor?

 

In which case it must be bonded.

 

One thing that a LOT of people miss is that if a metallic service such as a water pipe leaves the equipotential zone and then re-enters the equipotential zone at another point, it must be bonded at that point too.

So if a pipe goes under a ground floor, then up again, it must be bonded where it re-enters.

Share this post


Link to post
Share on other sites
Evans Electric

I have never heard  that  mentioned ,   since bonding was introduced  TBH .:C 

Share this post


Link to post
Share on other sites
kerching
9 hours ago, Evans Electric said:

I have never heard  that  mentioned ,   since bonding was introduced  TBH .:C 

I have....didn't we discuss it on here years ago?

some industrial units that were formed out of a common steel frame but services kept ducking underground ?

 

i think,it  Was 15th update course I went on where it was suggested we drill bottom flange of a wet Rad and fit a nut and bolt....then those little rad clamps came out.

 

also at same time there were some PLASTIC BS951 clamps!.....seriously, possibly by Erico, came in a yellow plastic bag. Looked like hose/washing machine ratcheting pipe clamp

 

 

 

 

 

 

and they still make them!!!!!!!

 

IMG_4227.thumb.PNG.bc503d9cd6bf529b6a41b7efc869d550.PNG

Edited by kerching

Share this post


Link to post
Share on other sites
Tony S
23 hours ago, Sidewinder said:

In which case it must be bonded.

 

One thing that a LOT of people miss is that if a metallic service such as a water pipe leaves the equipotential zone and then re-enters the equipotential zone at another point, it must be bonded at that point too.

So if a pipe goes under a ground floor, then up again, it must be bonded where it re-enters.

 

I’ve known about it but not in a domestic scenario. Our works gas mains would be bonded at each entry point to the plants LV MET.

 

MET? I don’t think anyone could say where one ended and another began, they were all linked by the 11kV system.

Share this post


Link to post
Share on other sites
SPECIAL LOCATION
On 01/02/2019 at 23:35, Sidewinder said:

In which case it must be bonded.

 

One thing that a LOT of people miss is that if a metallic service such as a water pipe leaves the equipotential zone and then re-enters the equipotential zone at another point, it must be bonded at that point too.

So if a pipe goes under a ground floor, then up again, it must be bonded where it re-enters.

 

13 hours ago, Evans Electric said:

I have never heard  that  mentioned ,   since bonding was introduced  TBH .:C 

 

It has been mentioned in the OSG since 2011..

 

ie.  Buried internal metallic pipe work re-appearing is mentioned in section 4 Earthing & bonding...

 

Pg 48 in the current Blue book..

Pg 44 in previous Yellow book

Pg 40 in the Green 17th Ed Amd 1 2011 OSG....

 

Basically saying it should be considered extraneous, the same just as incoming service pipes therefore requires bonding.

 

 

Guinness

 

Share this post


Link to post
Share on other sites
sprocketflup

Can you guys recommend me some further reading? Im missing something 

 

The scenario of a pipe going into the ground and reappearing somewhere else in the house, in reality how much potential difference are we likely to see between two areas of the same house?

Share this post


Link to post
Share on other sites
Sidewinder

Look at GN8 & GN5 as a start.

Share this post


Link to post
Share on other sites
binky

@Evans Electric the requirement to bond metallic pipework  enetering an equipotential zone ie house, was always to  negate the potential to have differing earth potentials within the same building. ie DNO earth versus what is effectively a very large earth rod. Hence under fault conditions, all extranuous conductive parts within said equipotential zone would be at the same touch voltage, and that touch voltage should not exceed 50V. 

Share this post


Link to post
Share on other sites
Tony S

OK I’ll put this in to a personal situation.

 

To get gas to the boiler and fire in my house I had to go under the solid kitchen floor with the main household gas pipe. The pipe was layed in a sand filled trench with a bitumen topping, continuous copper pipe throughout. Bonding at the gas meter was 7/064 (16mm), should I have bonded the copper pipe again at the point it re-immerged from the floor?

Share this post


Link to post
Share on other sites
Sidewinder
9 hours ago, Tony S said:

OK I’ll put this in to a personal situation.

 

To get gas to the boiler and fire in my house I had to go under the solid kitchen floor with the main household gas pipe. The pipe was layed in a sand filled trench with a bitumen topping, continuous copper pipe throughout. Bonding at the gas meter was 7/064 (16mm), should I have bonded the copper pipe again at the point it re-immerged from the floor?

Strictly speaking bs 7671 requires that the pipe is bonded at every point of entry into the equipotential zone.

So it should have been bonded.

 

Share this post


Link to post
Share on other sites
binky

but there's far more copper in that pipe than the bond, ergo pointless - clerly test to prove, but from an electrical continuity point of view both points are very well linked.

Share this post


Link to post
Share on other sites
Sidewinder
1 hour ago, binky said:

but there's far more copper in that pipe than the bond, ergo pointless - clerly test to prove, but from an electrical continuity point of view both points are very well linked.

I didn’t say that it wasn’t pointless, I said that for strict compliance it’s necessary.

Share this post


Link to post
Share on other sites
SPECIAL LOCATION

For the average domestic property these re-emerging pipes scenarios are as Binky suggests a very low level risk....

 

But I think the key point is.....

 

The average domestic property.. is NOT every possible type of installation... 

e.g. in some larger domestic (and of course non-domestic) situations a re-emerging pipe could be a whole different ball game..

 

So bottom line is...  as with 99% of electrical work,  that there is NO "one-size-fits-all" solution..

 

It is a situation everyone should be aware of..

Do whatever tests they consider necessary..

Take carful consideration of BS7671..

 

Then decide if or what to bond as appropriate...

Fill in & sign your certificate, with any relevant comments/observations/deviations you consider appropriate..

 

At the end of the day, it will only be if or when A.N.Other is seriously (or fatally) injured due to your electrical work , that someone will start questioning your judgment?

 

To ignore re-emerging pipes without any consideration of BS7671 shows a lack of understanding of the regs we work to IMHO..

 

Guinness

 

 

 

Share this post


Link to post
Share on other sites
binky
1 hour ago, Sidewinder said:

I didn’t say that it wasn’t pointless, I said that for strict compliance it’s necessary.

would I be right in thinking we could risk assess it as uneeded?

Share this post


Link to post
Share on other sites
Evans Electric

In a similar vein I'm intrigued  by the attitude  towards  plastic fittings onto copper pipes  .

 

We started off  bonding water just above the main stop valve  , this effectively covered all the pipework in a house  and  with  gas done the same everyone seemed happy .

 

Then  after some years  we're on a domestic  with the builder ,  I attached the 10mm  in the prescribed position  and  returned  to the floor above .  The  plumber joins us , cuts the pipe I just bonded & inserts a plastic  tee  , announcing that these are the future.  

  Not having seen them before , we even tested across the tee ,  knowing how "important"  bonding is ...thinking there may be a jumper inside ...there is'nt .  Like fools we  put a jumper across  ,  the plumber asked if we doing every one he fits ...answer  erm..well no . 

 

So after the tee was inserted  all we had bonded was  2m  of copper  rising up to the floor above.

 

Being me , I made a call to the Electric Police  who fobbed me off with " Why are you worrying about it ?"      I made a few more enquiries to be told to just do my job , run the  10mm , bond above the stop tap  , and  ..apparently ... it doesn't matter anymore about  the pipework throughout the job  as I keep banging on about :C

 

It doesn't occur with gas as all the fittings are metallic ...but I notice that gas fitters often leave a card warning the customer that bonding should be installed ,  and have indeed been called in to do it .      

Share this post


Link to post
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now

×

Important Information

Terms of UseWe have placed cookies on your device to help make this website better. You can adjust your cookie settings, otherwise we'll assume you're okay to continue.