No local isolation

Recommended Posts

SLIPSHOD & SLAPDASH

No isolation except  the supply circuit breaker for  external  A/C units, no manufacturers instructions . Is this always a C2  It is in my eyes but checking before i   complete a report, that anyone may have a reason its a C3

Share this post


Link to post
Share on other sites
Andy™

MCB can be used for isolation so no code

 

table 537.4

Edited by Andy™

Share this post


Link to post
Share on other sites
Murdoch
58 minutes ago, Andy™ said:

MCB can be used for isolation so no code

 

table 537.4

 

Agree with the above but this is a glaring issue now we have RCD's ................ how can you provide DP isolation using a MCB to "rule out" a fixed appliance being the cause of a RCD trip?

Share this post


Link to post
Share on other sites
Sharpend

Isn’t there a requirement for local isolation within 2m of equipment for maintenance purpose? 

I know all our AC installs have an isolators adjacent to outdoor unit. 

Edited by Sharpend

Share this post


Link to post
Share on other sites
binky

Never seen AC without a local isolator, think I would agree it's bad practice to rely on MCB as this does not isolate Nuetral. C2, not sure? 

Share this post


Link to post
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now

×

Important Information

Terms of UseWe have placed cookies on your device to help make this website better. You can adjust your cookie settings, otherwise we'll assume you're okay to continue.