Jimbo8

Voltage on earth ar cu when earth disconnected from earth bar and mcb on

Recommended Posts

Jimbo8
8 hours ago, Sharpend said:

Let’s stop right there shall we? jimbo you have asked a question that has been answered, it has also been suggested that you’re actions are dangerous, you for some unknown reason now want to turn the good advice into something bad as if you’ve been insulted or attacked? 

We all have to learn and if it’s something you don’t understand that’s fine but to insult those that are trying to educate you then that’s not right. 

 

If there is something else about this that you don’t understand then please ask, otherwise try to understand the advice you’ve been given. 

 

Getting defensive serves no purpose other than to prevent people gaining assistance when needed. 

I wasnt being rude to him I was just asking for advise if anyone had seen this before all the best 

Share this post


Link to post
Share on other sites
Murdoch
21 hours ago, Jimbo8 said:

Hi Murdoch just in twenty plus years of doing this and have never seen it before I wonder how many sparks have never noticed this with the earths I understand what ur both saying and not to disconnect earths while mcb is on but how would we ever know this is happening  if I never did do it 

 

Hum .........

 

My MFT, if I try and do a Zs and get odd looking voltages displayed on the screen either L-N or L-E , and it refuses to do the test - is usually symptomatic of a floating N or E. 

 

Odd you've not seen this in 20 years on the tools. Floating neutrals are often why lights don't work!

Share this post


Link to post
Share on other sites
Rob.
4 minutes ago, Murdoch said:

 

Hum .........

 

My MFT, if I try and do a Zs and get odd looking voltages displayed on the screen either L-N or L-E , and it refuses to do the test - is usually symptomatic of a floating N or E. 

 

Odd you've not seen this in 20 years on the tools. Floating neutrals are often why lights don't work!

 

Thing is, this isn't likely now that we have had further information a floating neutral. (Although was my first thought with the limited original information provided).

 

It's likely earth leakage from a device being powered by the circuit. 

 

Most electricians wouldn't notice this, as they would switch the circuit off to move the CPC in the consumer unit. 

Share this post


Link to post
Share on other sites
Jimbo8
17 minutes ago, Murdoch said:

 

Hum .........

 

My MFT, if I try and do a Zs and get odd looking voltages displayed on the screen either L-N or L-E , and it refuses to do the test - is usually symptomatic of a floating N or E. 

 

Odd you've not seen this in 20 years on the tools. Floating neutrals are often why lights don't work!

My tester wont ket me do test if voltage not correct I meant not seen voltage on earths before but like I say never disconnected earth before either was just a off chance that i did and noticed it 

10 minutes ago, Rob. said:

 

Thing is, this isn't likely now that we have had further information a floating neutral. (Although was my first thought with the limited original information provided).

 

It's likely earth leakage from a device being powered by the circuit. 

 

Most electricians wouldn't notice this, as they would switch the circuit off to move the CPC in the consumer unit. 

That's very true rob pal all I'm asking is anyone else seen this and if so what was there  findings thanks 

Share this post


Link to post
Share on other sites
Sidney

Any loads on the circuit?

Share this post


Link to post
Share on other sites
Jimbo8
3 hours ago, Sidney said:

Any loads on the circuit?

No pal nothing 

Share this post


Link to post
Share on other sites
Jimbo8
On 02/09/2019 at 08:34, Rob. said:

If you got an actual spark, this is suggesting a more sinister fault. 

 

A floating capacitive voltage, shouldn't have enough energy to produce a visible spark. 

 

All other circuit testing ok? 

 

TNCS earthing by any chance?

Yes rob pal it is a tncs I believe the reason behind this is because neutral  earth combined and disconnecting earth would become live because off connection to neutral 

Share this post


Link to post
Share on other sites
Sidney

Could be a high resistance joint on the neutral between the head and DB.

Share this post


Link to post
Share on other sites
Jimbo8
1 hour ago, Sidney said:

Could be a high resistance joint on the neutral between the head and DB.

It's because it's a tncs earth system if you disconnect the earth while cct on the voltage will be there because its connected to neutral at the head 

Share this post


Link to post
Share on other sites
binky

if cct is energised it induces votage in the CPC as mentioned above. I've had small sparks on CPCs before, turning cct off normally stops this! I have spent many hours puzzling non-issues because I've done things out of normal sequence. 

Share this post


Link to post
Share on other sites
Jimbo8
On 05/09/2019 at 21:41, binky said:

if cct is energised it induces votage in the CPC as mentioned above. I've had small sparks on CPCs before, turning cct off normally stops this! I have spent many hours puzzling non-issues because I've done things out of normal sequence. 

Yes binky  it was a head scratch pal never seen it before has I always turn cct off just forgot on this occasion  thankfully it was in my house with no one here but just shows we are all still learning no many sparks seen this by the comments 

Share this post


Link to post
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now

×

Important Information

Terms of UseWe have placed cookies on your device to help make this website better. You can adjust your cookie settings, otherwise we'll assume you're okay to continue.