Bathroom extractor fan

Question

corax

Hello

 

Wondering if someone can give me some advice. I have an s&p td silent fan that I want to use as a bathroom extractor fan. I'm looking to run the fan (no timer or humidistat) from a switch outside the bathroom by turning the existing 1 gang light switch to a two gang. Is this possible? Would I just connect the fan cable to the 2nd gang of the switch?

 

Thanks in advance for any insight

Share this post


Link to post
Share on other sites

23 answers to this question

Recommended Posts

  • 0
Geoff1946

Depends if the circuit neutral is also available in the switch box.

Share this post


Link to post
Share on other sites
  • 0
ProDave

.... and the practicality of getting a new cable from the switch to the fan, which depending on the house construction may mean chasing a new cable into the wall.

Share this post


Link to post
Share on other sites
  • 0
corax

should be easy enough to get the cable from the switch to the fan as have plasterboard walls

Share this post


Link to post
Share on other sites
  • 0
Murdoch

Out of interest why do you want it on a seperate switch?

 

Share this post


Link to post
Share on other sites
  • 0
ProDave
3 minutes ago, Murdoch said:

Out of interest why do you want it on a seperate switch?

 

I have always done that in my own house, so you can go for a pee in the night without the fan noise, and only use the fan when showering (or making a smell)

 

Never do it in a rented property, tenants can't be trusted to actually use the fan when showering,  for them it has to be automatic with no way to turn it off (no fan isolator switch)

Share this post


Link to post
Share on other sites
  • 0
binky

I like 2 lights in bathrooms, main lighting and a dimmer single  light (can be something like an illuminated mirror) for those midnight piddles.

Share this post


Link to post
Share on other sites
  • 0
kerching
1 hour ago, binky said:

I like 2 lights in bathrooms, main lighting and a dimmer single  light (can be something like an illuminated mirror) for those midnight piddles.

For the purpose of nocturnal micturation  I have a PIR in the ceiling. This switches 1 LED mini spot mounted in the wall at low level adjacent to the bog. This also has the advantage that when the grandchildren visit they are not searching for a switch, they just go in and on comes the light. Simples.  Saves them having to remember to switch it off afterwards as well

Share this post


Link to post
Share on other sites
  • 0
Murdoch

The way I did ours, is the light over the shower and the fan are on 1 (short) pull cord and the other lights are on a 2nd (longer) pull cord. Then there is the option of the illuminated cabinet too.

Share this post


Link to post
Share on other sites
  • 0
corax

OK so on further inspection getting a cable up through the wall is not that easy. As an alternative can I just power the fan from one of the existing 50w downlights? i.e. run a two core cable from the live and neutral of the downlight to the live and neutral of the fan?

Share this post


Link to post
Share on other sites
  • 0
Murdoch
Just now, corax said:

OK so on further inspection getting a cable up through the wall is not that easy. As an alternative can I just power the fan from one of the existing 50w downlights? i.e. run a two core cable from the live and neutral of the downlight to the live and neutral of the fan?

 

 

Probably, and being perdantic it needs to be 3 core 

 

oh, and  1 further question - are your lights LV or 230v?

Share this post


Link to post
Share on other sites
  • 0
corax

they are 230v GU10's. What would I use the 3rd core for? There doesn't seem to be any earth for the fan and on the downlights the earth is just folded back..

Share this post


Link to post
Share on other sites
  • 0
Murdoch
Just now, corax said:

they are 230v GU10's. What would I use the 3rd core for? There doesn't seem to be any earth for the fan and on the downlights the earth is just folded back..

 

do you have a copy of the regs? 

Share this post


Link to post
Share on other sites
  • 0
corax

Hello, no was hoping this was a diy job to be honest, would you recommend getting someone in?

Share this post


Link to post
Share on other sites
  • 0
Murdoch
Just now, corax said:

Hello, no was hoping this was a diy job to be honest, would you recommend getting someone in?

 

There is a requirement to provide an earth at every point in a 230v circuit and continuity of which needs to be confirmed back to the fuseboard. This is especially important in bathrooms. 

 

I would recommend you get this checked by a spark with a suitable tester - and just for good measure all changes to lighting circuits require RCD protection.

 

Hope this helps

Share this post


Link to post
Share on other sites
  • 0
corax

ah ok, sounds like this job is maybe a bit beyond me then. Thanks for the info

Share this post


Link to post
Share on other sites
  • 0
Evans Electric

1)   If you wire fan from a downlight , it will only work while the lights are on .

 

2)  If you get a  cable down to your wall switch and a  neutral from  one of the lights  you can switch it on  & off at the wall .  

 

As said above  ,  as electricians we are obliged to work to the Regs ...generally speaking   DIYers  do  as they like . 

 

 

Edited by Evans Electric

Share this post


Link to post
Share on other sites
  • 0
Murdoch
Just now, corax said:

ah ok, sounds like this job is maybe a bit beyond me then. Thanks for the info

 

Maybe post your location and see if anybody on here is close to you?

Share this post


Link to post
Share on other sites
  • 0
corax

sure am in East Lothian here, let me know if anyone is in the area

Share this post


Link to post
Share on other sites
  • 0
Risteard
57 minutes ago, Murdoch said:

 

 

Probably, and being perdantic it needs to be 3 core 

 

oh, and  1 further question - are your lights LV or 230v?

Being pedantic 230V is low voltage.

Share this post


Link to post
Share on other sites
  • 0
Murdoch
34 minutes ago, Risteard said:

Being pedantic 230V is low voltage.

 

You know that, I know that.

 

Joe Public thinks 12v is low voltage

Share this post


Link to post
Share on other sites
  • 0
Evans Electric

So do I  TBH   .      I 've always thought the change to calling 240V    "Low Voltage"   is one of the most  ludicrous ideas ever  mooted by the IEE   .    

Share this post


Link to post
Share on other sites
  • 0
kerching
49 minutes ago, Evans Electric said:

Low Voltage"   is one of the most  ludicrous ideas ever  mooted by the IEE   .    

Oh, I don't know....forgetting to put RCD sockets and Spurs into the 18th edition I think must come close to the winning post

Share this post


Link to post
Share on other sites
  • 0
Evans Electric

Photo finish  there then !! 

Share this post


Link to post
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now

×

Important Information

Terms of UseWe have placed cookies on your device to help make this website better. You can adjust your cookie settings, otherwise we'll assume you're okay to continue.