Jump to content
simon-0116
Wylex rcd button not working
Recommended Posts
simon-0116
Wylex split load board, installed 2 weeks ago
Field called me on a Sunday afternoon saying 1 side tripped and now he's resett it but test button dosn't work.
So I grab a spare rcd a few tools the wife and kids as they very mad about helping a good friend.
Test rcd button and times. Button dosn't work and 1x above 310ms.
So swap rcd to another and same results.
When you plug something in on socket circuit it trips rcd now,  he says wasn't before.
Insulation at 250v live neutral + e above 200
My wife going mental so agree with mate I'll go back on Monday
Coincidence both rcd faulty or am I missing something.
Am I been thick over looking something simple
Edited by simon-0116
Share this post
Link to post
Share on other sites
Andy™
neutral in the wrong bar or N-E fault
Share this post
Link to post
Murdoch
I would suggest you disconnect ALL the neutrals from the relevant neutral bars, turn off all the MCB's, and test the RCD properly with your MFT
IME RCD's rarely fail in service, especially  after such a short period of time
N-E fault likely
PS - RCBO boards are far better...
Edited by Murdoch
Share this post
Link to post
binky
check PSCC/ PFC - look for faulty incoming neutral, anything weird is usually a neutral!
Share this post
Link to post
Murdoch
Like that.
Reminds me of a fault a couple of years ago a customer was experiencing their rcds tripping ... often together. There was a plug below the board so I plugged my MFT in and looked at the voltages L - N and L - E ..... the L -N was fluctuating ....
so I called the dno ... at 7pm they turned up, at 3 am a temporary generator was installed and the next day they dug up the neighbours patio .... to repair the damaged incoming supply
Issues like this make the job so very interesting
Share this post
Link to post
binky
confused the lettuced out of me the first time I encountered a DNO neutral fault...
Share this post
Link to post
Create an account or sign in to comment
You need to be a member in order to leave a comment
Create an account
Sign up for a new account in our community. It's easy!
Register a new account
Sign in
Already have an account? Sign in here.
Sign In Now
Important Information
Terms of UseWe have placed cookies on your device to help make this website better. You can adjust your cookie settings, otherwise we'll assume you're okay to continue.