Building a 600 amp service. 120/208 Volt. What size conductors and riser conduit would be required? Can the conductors be in the same riser or in separate risers. I was thinking 350 MCM in parallel on each supply  leg feeding (4) 350 MCM polaris connectors. The 4" weatherhead only has 7 knock outs in it and I need 8.
Share this post
Link to post
kerching
Well using my powers of psychic deduction you are NOT in Gods own Country ( the UK) but some foreign land.   We don't do 120/208V so I'm guessing your Regs are different to ours so we probably cannot help
but I may well be wrong
Share this post
Link to post
Andy™
something large enough that doesnt melt when its under load of 600a
Share this post
Link to post
Evans Electric
No  doesn't make much sense to either ,  I'm guessing  Mr  IES  is in the US   .....he is of course  most welcome here  but there are some vast differences  between our method and terminology.
Share this post
Link to post
Tony S
If you’re using taps-offs fr'om the riser then as far as I recall you have to rate the riser for the total fault current. Separate risers then you have to use the NIC tables taking in account separation and support points.