Just to try and explain a bit more for you Traineeboy.....
Remember that the reason for checking what the PFC is...
is to verify that a worst-case short circuit fault should not generate a fault current greater than the breaking capacity of any protective devices connected to the supply...
And..
Back to your basic science theory, the nearer you are to the supply...
The higher the PFC will be...
So the further into an installation you go the PFC will either be equal or less than the PFC at the origin..
As an exercise... do the PFC at you main DB and your garage DB..
see what, (if any) difference you get?
Which is why as others have said..
You would normally just note down the PFC at origin...
Even though.... for some reason that I don't understand...
Back in the 17th Ed, Red Book, (valid from July 2008 -> ),
and earlier, the Schedule of test results model form just says "PFC.............kA"
Whereas from the Green book, (valid from Jan 2012 -> ),
onward it then said "Ipf at DB (kA).............................."
Guinness
dunno if that helps.. or not???
:C
But keep your questions coming...
always good to see someone who genuinely wants to learn, asking questions whilst clarifying what they do or do not already understand..