pedg

Member
Joined
Jul 18, 2020
Messages
14
Reaction score
3
Hopefully this is the right place to ask this question. Apologies if not.

We need to get our 60A main fuse upgraded to a 100A fuse to handle the addition of battery storage and EV charge point.

Due to various rules it appears we need someone from the power supply company, someone from the people we are buying electricity from and our own electrician there at the same time as each is only allowed to change things in their own areas?

What power company and provider need to do is, I think, clear, if perversely over-regulated (provider adds bigger wires to the meter so that power company person can connect them to new fuse). My confusion is about what I need our electrician (once we can get hold of one) to do? Power company says they would need to upgrade cable between the meter and the consumer unit but our current set up is more complicated than that.

(apologies if not using the right terms).

Currently meter goes to a junction box where the solar PV comes in. Then another ongoing cable goes, via an 80A RCCB, to a second junction box. Off this are the main consumer unit,  subunit for the outhouse and currently redundant connection which we hope to use for the battery and EV connections.

My guess is that we need to upgrade the cable from meter to first junction box, the cable from that junction box to second junction box and the RCCB with something that can handle a higher amperage. Beyond the second junction box none of the things connected should be drawing anything near 100A individually so would hope/assume not of the other wires need upgrading?

So question is what do we need to get an electrician to do to appease the power supply company (UK power networks as in Cambridge)?

Thanks for any help.

 
Any chance of some pictures?, I think as a new user here, you'll have to upload them somewhere on the www and link them here as I dont think you can upload to here until you have x amount of posts....

 
I am not sure why your energy supplier needs to be involved in the mix.

FIRST thing is your spark upgrades the outgoing meter tails to your consumer unit(s) and ensures all of that is up to standard.  That will involve cutting the seal on the meter (if there ever was one).

Then the DNO will come and upgrade the tails from their supply head to the meter and re seal everything.

They don't need to be there at the same time,  in fact that would be a bad plan as the DNO is not going to wait around for your electrician so he can re seal the meter.

That's how it would work here in SSE land, I know some other DNO's have other ideas.

There are some ways to make it work easier.  A good one here is don't mess about trying to ask for upgrades.  Get your electrician to do your tails, then your electrician phones the DNO and reports a dangerous condition (note the D word) reporting substandard tails.  That will usually get them out quick.

 
Last edited by a moderator:
I think you need to get a local spark or 2 to advise you
I am trying to but want to get a better handle on what to ask them.

Any chance of some pictures?, I think as a new user here, you'll have to upload them somewhere on the www and link them here as I dont think you can upload to here until you have x amount of posts....
Tails from meter go into this block that links in the solar: https://photos.app.goo.gl/dmnWKoQUN3Njk6HHA

Ongoing cable goes through this RCCB: https://photos.app.goo.gl/KyDwMWit95uasE6o6

Into this block that then goes onto consumer unit, sub unit, etc: https://photos.app.goo.gl/at2Rtuq62Q3v2zBW9 (I paraphrased a bit as currently have one spare (old shed connection), one now used for solar bypass, (old power show connection). Plan is to combine this into one subunit with the battery and EV connections)

I am not sure why your energy supplier needs to be involved in the mix.

FIRST thing is your spark upgrades the outgoing meter tails to your consumer unit(s) and ensures all of that is up to standard.  That will involve cutting the seal on the meter (if there ever was one).

Then the DNO will come and upgrade the tails from their supply head to the meter and re seal everything.

They don't need to be there at the same time,  in fact that would be a bad plan as the DNO is not going to wait around for your electrician so he can re seal the meter.

That's how it would work here in SSE land, I know some other DNO's have other ideas.

There are some ways to make it work easier.  A good one here is don't mess about trying to ask for upgrades.  Get your electrician to do your tails, then your electrician phones the DNO and reports a dangerous condition (note the D word) reporting substandard tails.  That will usually get them out quick.
Apparently, as I understand it, the power distribution company own the fuse, the energy supplier owns the meter and we own everything after the meter. UK power networks appear to be more fussy than others about this from what i can see.

Also my question is that the meter tails do not go directly to the consumer unit and in this situation which parts need to be upgraded?

 
What area are you in? 
 

all you need is to ask a local spark - ask work colleagues, family neighbours who they have used - if they will take a look to see if your existing meter tails need upgrading for a 100A supply. Leave the rest to the spark to advise. Shouldn’t take that long to do if he/she is competent. 
 

then arrange for DNO to carry out upgrade of their cabling if required, as Dave hinted at there are ways to get it done pronto if it’s not already prearranged. The DNO may well upgrade the fuse for you at same time, although not always. It’s more about who comes out. 
otherwise you will have to request the upgrade from the DNO in which case there may be a charge? 
 

 
Apparently, as I understand it, the power distribution company own the fuse, the energy supplier owns the meter and we own everything after the meter. UK power networks appear to be more fussy than others about this from what i can see.

Also my question is that the meter tails do not go directly to the consumer unit and in this situation which parts need to be upgraded?
There is no consistency in supply companies.  the worst I found was N Power who would not take a telephone report of an urgent dangerous condition and demand I put the request in writing.

As to which part of your tails to upgrade.  ALL of them should be upgraded to 25mm. It might be a good opportunity to get rid of some of the junctions and tidy things up.

 
We need to get our 60A main fuse upgraded to a 100A fuse to handle the addition of battery storage and EV charge point.

Thanks for any help.


Battery shouldn't affect main incoming supply, not so sure about EV charge point, but I'm interested to know who said this? 

 
What area are you in? 
 

all you need is to ask a local spark - ask work colleagues, family neighbours who they have used - if they will take a look to see if your existing meter tails need upgrading for a 100A supply. Leave the rest to the spark to advise. Shouldn’t take that long to do if he/she is competent. 
 

then arrange for DNO to carry out upgrade of their cabling if required, as Dave hinted at there are ways to get it done pronto if it’s not already prearranged. The DNO may well upgrade the fuse for you at same time, although not always. It’s more about who comes out. 
otherwise you will have to request the upgrade from the DNO in which case there may be a charge? 
 
In Cambridge so UK power network the DNO. Tried a number of sparks but most end up at the 'We will get back to you" stage that never happens and with various things a bit up in the air I have not got round to rehassling any of them but will try again.

Battery shouldn't affect main incoming supply, not so sure about EV charge point, but I'm interested to know who said this? 
You can charge the battery from mains as well as from the solar. Obviously only really of use if on a variable tariff. Intending to move to octopus agile tariff so on the rare times they pay you to use electricity could well be wanting to put 16A into the battery and 32A into the EV at the same time.

Basically I think my question best asked as 3 separate questions:

1) How much of the wiring would need to be upgraded to 25mm for the DNO to be happy given I don't have wires going directly from the meter to consumer unit? Given max current from each branch from the final junction box would be under 60A individually assume 25mm through to that junction box should be fine?

2) Can I get a spark in to do the upgrades from the meter onwards before the other changes? (supply company promise to attend at the same time as the DNO to do their bit). 

3) What should I have the 80A RCCB replaced with?

 
If you get up to 10 posts you can post pictures ............

That rather depends on the size of the DNO fuse ..........
Going from a 60A fuse to 100A fuse so current 80A RCCB one assumes is going to be too small.

 
You can charge the battery from mains as well as from the solar. Obviously only really of use if on a variable tariff. Intending to move to octopus agile tariff so on the rare times they pay you to use electricity could well be wanting to put 16A into the battery and 32A into the EV at the same time.


OK so it's an AC battery set-up, and you are looking for the potential to charge battery and EV on off-peak tariffs, when it is unlikley you will be pulling any other large loads unless you have night storage heaters. Probably find 60A main fuse is fine as it is. If you wanted a bit of extra headroom, replace with 80A, that way, and I'm guessing your existing tails are16mm,  everything else would be fine as they are. 

 
OK so it's an AC battery set-up, and you are looking for the potential to charge battery and EV on off-peak tariffs, when it is unlikley you will be pulling any other large loads unless you have night storage heaters. Probably find 60A main fuse is fine as it is. If you wanted a bit of extra headroom, replace with 80A, that way, and I'm guessing your existing tails are16mm,  everything else would be fine as they are. 
Actually with the Agile tariff the cheapest periods are often mid-afternoon before peak period starts at 4pm (usually), which makes it useful for topping up the battery before the peak period (e.g. see today's here: https://twitter.com/energystatsuk/status/1285594671645970433/photo/1). Also for the occasional periods when the tariff goes negative, i.e. you are paid to use the electricity, would like to have enough overhead to do things like have the washing machine, tumble drier, dishwasher etc on at the same time to make the most use of it.

 
Hmm,

Hate to say this, but before you get too carried away, it is VERY far from certain that the DNO will give you a bigger supply...

john..


When we last had our meter replaced they also downrated the main fuse from 100A to 80A...

Which is around about 18.5kVA...

I asked why, they basically said it was now routine policy not to fit 100A to a standard domestic installation...

Guinness    

 
Last edited by a moderator:
Hmm,

Hate to say this, but before you get too carried away, it is VERY far from certain that the DNO will give you a bigger supply...

john..


Their website here https://www.ukpowernetworks.co.uk/electricity/fuse-upgrade appears to imply its a standard operation but possibly not then? As it says " Our expert will visit you to advise what is possible at your property." I have messaged them to get someone out to look at it to see what they say. 

 
Actually with the Agile tariff the cheapest periods are often mid-afternoon before peak period starts at 4pm (usually), which makes it useful for topping up the battery before the peak period (e.g. see today's here: https://twitter.com/energystatsuk/status/1285594671645970433/photo/1). Also for the occasional periods when the tariff goes negative, i.e. you are paid to use the electricity, would like to have enough overhead to do things like have the washing machine, tumble drier, dishwasher etc on at the same time to make the most use of it.


Not looked at tariffs for a long time, very interesting and all part of the 'smart network' they have been talking baout for years. Even with all the appliances running you are unlikley to top 80A - your solar panels wil help with that.. The main fuse will take some temporary power spikes at higher than 80A for shortish periods of time. Things like washing machines when not heating water will run at around 250W, so I would feel 80A is probbaly fine.  John is correct though, they won't necessarily give you 100A as it depends on the house feed, but only the local DNO can advise you of that. Around my way, 80A is normal, and I have 60A being an older house. 

 
Not looked at tariffs for a long time, very interesting and all part of the 'smart network' they have been talking baout for years. Even with all the appliances running you are unlikley to top 80A - your solar panels wil help with that.. The main fuse will take some temporary power spikes at higher than 80A for shortish periods of time. Things like washing machines when not heating water will run at around 250W, so I would feel 80A is probbaly fine.  John is correct though, they won't necessarily give you 100A as it depends on the house feed, but only the local DNO can advise you of that. Around my way, 80A is normal, and I have 60A being an older house. 


Interesting thing about these tariffs is it makes having a battery system a viable option even for those people without solar as you can cover the expensive period by timeshifting power from a cheaper period that will take 30 to 50% off the electricity bill. For us the combination of summer savings via the solar and winter savings via timeshifting power means it will pay for itself several years sooner than just via the solar, the duration of which was what had been putting me off beforehand. My rough estimate brings it down from about 12 years to 8 but will not know for sure until it's (eventually!) used in anger.

I think I am moving towards the 80A option. Once the battery system up and running will be able to better monitor energy usage via its CT clamp on the main cable so will be able to see how high it does go (current 'smart' meter has self lobotomized itself so of no use at the moment). For the AC inverter I have there is some software that both reports current data and allows it to be controlled programmatically. Was going to use this to try and automate when it charged from the mains but probably sensible when it is set to do that to keep an eye on the power been drawn from the grid so it can I can turn it off again if the current gets close to 80A.

 