Jimip

MCB/RCD on consumer unit tripping

Recommended Posts

Jimip

When we use our microwave the ‘sockets’ RCD trips on the consumer unit.
The microwave starts and runs for about2-3 seconds before it trips. If we use the microwave on medium power all is fine. This has been happening for a couple of years.

Microwave has been into the service centre  in the electrical retailers I work at and had every test he could think of and couldn’t fault it.
Today I’ve moved it to a different socket in the kitchen with same result. Then tried socket in conservatory that goes through its own consumer unit. In there it worked fine on full power but sockets in house had still tripped.

At a bit of a loss as to what to look at next?

Been suggested I could change the RCD to one that gives a slight time lag similar to a slow blow fuse?

any suggestions please?

 

Share this post


Link to post
Share on other sites
Andy™

RCD's are designed to trip within a specific time, so you wont find a 'time lag' one. best thing would be to get someone competant to do some fault finding rather than replacing random parts that you dont know anything about...

Share this post


Link to post
Share on other sites
boltonsparky

A time delay RCD isn't suitable for the use you intend. 

 

I doubt there is much wrong with the microwave itself (proven by the testing done on it) and the problems you are experiencing are due to a build up of earth leakage from various sources, the microwave just tips it over the edge. 

 

As mentioned by Andy you need to get somebody competent in to test the rest of the installation. They'll be able to measure earth leakage of the installation and I'd bet on it being higher than it should be and the microwave adding just enough to send it over and trip. It may also be that the RCD is over sensitive which a ramp test would eliminate. 

 

A very basic way of indicating if it is build up of leakage from multiple sources is to unplug everything in the house and just try the microwave on its own but this won't test the installation itself and isn't a substitute for proper testing. 

Edited by boltonsparky

Share this post


Link to post
Share on other sites
Murdoch

Sounds like you have 2 RCD's in series so the one in the main fuseboard will nearly always trip first.

 

The OP suggests the microwave works properly on a different installation

 

My suspicion is that your home has a lot of leaky devices and hence the microwave is tipping the RCD over its tripping point. 

 

If it was me investigating I would use my earth leakage clamp meter first and then do more tests on your installation, starting at the RCD ..........

Share this post


Link to post
Share on other sites
SPECIAL LOCATION

Sounds like classic symptoms of a poorly designed electrical installation..

lacking reasonable division of circuits across suitable protective devices as per regs 314..

 

Probably doesn't help when a further lack of 'what and how RCD's work' is thrown onto the mix..

 

I would bet both the appliance and the RCD are all working correctly..

and you actually have a problem of cumulative earth leakage across multiple sources/circuits..

 

Best solution is to start as per Andy's recommendation.

get someone competent to come and do some investigations / tests on your installtion..

 

:coffee

Share this post


Link to post
Share on other sites
Jimip

Thanks everyone for your responses.
 

Looks like it maybe more involved than I hoped!

 

With having easy access to a new microwave I will try that route first for simplicity but I will certainly get an electrician in to the check the system once the current climate allows.
 

 

Share this post


Link to post
Share on other sites
Fly Moose

For a home owner to test why not turn all your appliances off for the moment. Turn on the microwave. Full power. See what happens. If it works turn on each item one at a time then back off. in sequence. 

 

The culprit might be a fridge. 

 

This might guide you to a issue with another appliance....

 

But as said you may need a proper test on the circuit itself.

Share this post


Link to post
Share on other sites
SPECIAL LOCATION
1 minute ago, Fly Moose said:

For a home owner to test why not turn all your appliances off for the moment. Turn on the microwave. Full power. See what happens. If it works turn on each item one at a time then back off. in sequence. 

 

The culprit might be a fridge. 

 

This might guide you to a issue with another appliance....

 

But as said you may need a proper test on the circuit itself.

 

The above method of testing can be a bit hit & miss if there is, as I suspect, multiple circuits sharing the same RCD... 

e.g. traditional split-load or dual RCD board..

compared with a full RCBO board..

 

As you will have an abundance of parallel, Earth & Neutral connections permanently made at the CU...

 

And as a lot of devices don't incorporate double-pole switching..

Any current flowing from a perfectly good, appliance on circuit 'A' 'B' or 'C' can make its way to Earth via a dodgy N-E connection on circuit 'D'..

 

So you can end up leading yourself up a wild goose chase thinking it is the appliance you have just turned on that caused the trip!

 

      

Share this post


Link to post
Share on other sites
Fly Moose

The only reason I mention this was My fridge was on the way out and it did a similar thing when our lass used the oven. 

I concur with the assessment, but I was explaining as a trial and error for now. Leakage is getting rare in most properties with new technology, Most leakage is Kitchen based. A combination of items also trigger a trip as said. Yes a wild goose chase indeed. 

 

The other option I would have tried as a house holder(Not an electrician) turn off the other circuits on the side of the RCD leaving the kitchen circuit on. Then try again with full power on Microwave. Then do each circuit at a time see what happens. 

 

 

 

 

 

 

Share this post


Link to post
Share on other sites
Murdoch

Single or dual RCD boards are the work of the devil

 

RCBO boards are a must

Share this post


Link to post
Share on other sites
Fly Moose

Yes, and Hagar, are what we install, make a nice breaker sized one you can now do IR tests with them connected. No more removing from the board. 

Share this post


Link to post
Share on other sites
roys

I used SBS Daves RCBO’s, compact and double pole, no fly leads to deal with, they are nice and neat.

Share this post


Link to post
Share on other sites
boltonsparky
40 minutes ago, roys said:

I used SBS Daves RCBO’s, compact and double pole, no fly leads to deal with, they are nice and neat.

 

I've had a look at their stuff, it looks a really smart set up. They do the fire seal panel for the rear entry knockouts too which I was impressed with. Never had my hands on any of it though, it's always worked out more than locally sourced gear by quite a bit although they're fair priced I think compared to some. 

Edited by boltonsparky

Share this post


Link to post
Share on other sites
Murdoch
3 minutes ago, boltonsparky said:

 

I've had a look at their stuff, it looks a really smart set up. They do the fire seal panel for the rear entry knockouts too which I was impressed with. Never had my hands on any of it though, it's always worked out more than locally sourced gear by quite a bit although they're fair priced I think compared to some. 


since the 18th was implemented using single sourced fuseboard s is too much of a risk. 
 

the ones I fit , can be sourced from at least 3 vendors within 10 miles ....

Share this post


Link to post
Share on other sites
Andy™
3 hours ago, Murdoch said:


since the 18th was implemented using single sourced fuseboard s is too much of a risk. 
 

the ones I fit , can be sourced from at least 3 vendors within 10 miles ....

 

exactly, main reason why i wont install anything from a manufacturer/supplier that parts are not easily available

Share this post


Link to post
Share on other sites
Sidewinder
On 14/01/2021 at 18:33, Fly Moose said:

...

Leakage is getting rare in most properties with new technology, Most leakage is Kitchen based...

 

I disagree, with a lot of modern technology comprising of switched mode power supplies, leakage is increasing, thus, the requirement for this not to exceed 30% of the RCD rating, 531.3.2.

Share this post


Link to post
Share on other sites
kerching
19 minutes ago, Sidewinder said:

 

I disagree, with a lot of modern technology comprising of switched mode power supplies, leakage is increasing, thus, the requirement for this not to exceed 30% of the RCD rating, 531.3.2.

EXACTLY! So,why would anyone ever fit a dual RCD board!

in my humble and  , some would say , bigoted opinion they have never complied. Others may disagree, they are wrong, but are entitled to their opinion

individual RCBOs all the way

Share this post


Link to post
Share on other sites
boltonsparky
5 minutes ago, kerching said:

EXACTLY! So,why would anyone ever fit a dual RCD board!

in my humble and  , some would say , bigoted opinion they have never complied. Others may disagree, they are wrong, but are entitled to their opinion

individual RCBOs all the way

 

I'm all for RCBO boards now. Type A RCDs and scrap the previous versions 

 

Trouble is whilst the likes of screwfix and all are knocking out dual RCD boards with AC type RCDs for less that £70 that's what the majority of people will go for as price is king.

Share this post


Link to post
Share on other sites
Murdoch
1 hour ago, Sidewinder said:

 

I disagree, with a lot of modern technology comprising of switched mode power supplies, leakage is increasing, thus, the requirement for this not to exceed 30% of the RCD rating, 531.3.2.

 

agree 110%

 

Most leakage comes from the plethora of electronic goods around the home including modern kitchen appliances

 

AMD 2 , rather than faffing around with AFDD's and changing the distance a socket can be from a bath from 3m to 2.5m (I mean WTGrape) should mandate RCBO's for socket circuits IMHO

Edited by Murdoch

Share this post


Link to post
Share on other sites
Sidewinder

Instead, they have removed the allowance for risk assessment for socket circuits.

So for industrial (mainly) and commercial where you have loads such as machinery with designed in leakage then you are going to have an issue.

 

Share this post


Link to post
Share on other sites
Fly Moose

Nice to see you speak like electricians. Most people don't want to see anything new in there house unless it does something they can see. Or it makes them feel safe the ultimate question. 

 

How do you say its better and easy to solve a problem. RCBOs

 

 

Share this post


Link to post
Share on other sites
SPECIAL LOCATION
16 minutes ago, Fly Moose said:

How do you say its better and easy to solve a problem. RCBOs

 

 

If a customer had a single fuse protecting multiple circuits so in the event of a fault they wouldn't have a clue where the cause was coming from...

 

And it wiped out power to half or more of the property, possibly for several hours if they couldn't reset it easily...

And the fault happened late on a Saturday evening with no local electricians able to attend till Monday to try and get half or more of the property power back on again...

And the labour costs for investigating and tracking down the fault were three or four times more labour intensive as multiple circuits were involved..

 

They would say..

No way would I want anything as daft as that fitted!!

 

The same rules apply for RCDs -vs- RCBO's 

A multiple RCBO board is the most logical and cost effective solution..

 

And any single RCD protecting multiple circuits is the most stupid idea ever.. 

 

With the exception of possible an outbuilding, (Shed/Garage/Workshop), with a single RCD board..

Guinness

 

Share this post


Link to post
Share on other sites
Sidewinder
10 hours ago, Fly Moose said:

Nice to see you speak like electricians. Most people don't want to see anything new in there house unless it does something they can see. Or it makes them feel safe the ultimate question. 

 

How do you say its better and easy to solve a problem. RCBOs

 

 

As per the post by Specs above, and a single or dual RCD board does not comply with clause 314.1 of BS 7671

Share this post


Link to post
Share on other sites
Murdoch
4 minutes ago, Sidewinder said:

As per the post by Specs above, and a single or dual RCD board does not comply with clause 314.1 of BS 7671


hit, nail and head springs to mind BUT try discussing this with the typical person with a Screwfix catalogue on their kitchen table - all they want is the cheapest solution.

 

my tact is to quote for a RCBO board I will supply and fit  or I won’t do the job

Share this post


Link to post
Share on other sites
boltonsparky
26 minutes ago, Murdoch said:


hit, nail and head springs to mind BUT try discussing this with the typical person with a Screwfix catalogue on their kitchen table - all they want is the cheapest solution.

 

Exactly this, even wholesalers are still pushing them though, my local has a pile of schneider dual RCD's for around £70 each. 

 

As a budget upgrade against a very old non RCD board they offer a major improvement but in my opinion stop them being available and work on getting the RCBO prices down. Decent brand RCBOs are still north of £20, get them down to around £10 and they'd become an affordable option and most people would be converted. 

 

Unfortunately if they go with this AFDD rule in amd 2 there'll be very few boards getting changed by legit sparks, the no cert DIY Dave changes will be rife though. 

Edited by boltonsparky

Share this post


Link to post
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now

×

Important Information

Terms of UseWe have placed cookies on your device to help make this website better. You can adjust your cookie settings, otherwise we'll assume you're okay to continue.