I think it must be a designer idea but he or she should of refused as pipe is not earthed , way to small, bend radius too tight and no cable protection on entry or exit of pipe
Ā we normally do this to suite singles though. Personally I think I would have taken the pipe into the PVC box to allow a discreetĀ earth bondDo you think it would comply then? Itās installed in a restaurant toilet that I went to last night. You would never install Ā metal conduit that wasnāt earthed.