testing a motor prior to installation


NWDS

Question

Afternoon all, what two test should I carry out on a replacement motor ???. I have checked DOR and info on the plate all match the existing motor.

1 insulation resistance across L and N ( what range 500v dc/ 250v dc ) ?????

2 continuity of CPC to motor housing ???.

Can some one please advise.

Regards and thanks NWDS

Link to comment
Share on other sites
 

14 answers to this question

Recommended Posts

matt.leung

IR test - bridge over the motor controls..

Link to comment
Share on other sites
 
 
Evans Electric

For a 3 Ph motor , megger each pole to earth then megger between ( 500v) then read the resistance between the windings , usually if they are all the same the motor is OK.

Link to comment
Share on other sites
 

Thanks Evans, its a single phase motor, I was going to do the IR test on the windings ( across brown and blue ), I was then going to test contiuity of the earth connection by testing between the cpc and chasis, I would test these prior to fitting the motor to prove the motor is not faulty, am I on the right track.

NWDS

Link to comment
Share on other sites
 

Hi,

Before installation test winding resistance, then full IR live/Neutral Live/Earth Neutral/Live. then after installation test back to panel and fully test control and feed circuits, I know this sounds a bit long winded but you could fit a perfectly good motor and find that the control/feed circuit has been played with when the motor failed and someone whilst fault finding has put a wire back incorrectly and motor casing is live. then the big finger of blame gets pointed in your direction, better to spend an extra 30-40mins testing and be sure the motor and circuit is sound.

Link to comment
Share on other sites
 
Hi,

Before installation test winding resistance, then full IR live/Neutral Live/Earth Neutral/Live. then after installation test back to panel and fully test control and feed circuits, I know this sounds a bit long winded but you could fit a perfectly good motor and find that the control/feed circuit has been played with when the motor failed and someone whilst fault finding has put a wire back incorrectly and motor casing is live. then the big finger of blame gets pointed in your direction, better to spend an extra 30-40mins testing and be sure the motor and circuit is sound.

Sorry to revive an old thread but is this a continuity reading in ohms and what would this normally be for a healthy motor roughly.

Thanks

Link to comment
Share on other sites
 
mojorebel

single phase motor - would most likley be a spil phase - with a run and start winding- these have to be tested to earth and across winding- on a single phase the windingds will give a different reading (not balanced) should be a difference of about 20%

Link to comment
Share on other sites
 
 
 
seajayess

Why would you insulation resistance test between l/N these are connected together through the windings of the motor it should come back as a short circuit! I would take a continuity reading to make sure there was some form of coil of wire and on a 3 phase would make sure the readings were all about the same. You can do an insulation resistance test on a 3 phase motor between the windings but first you must remove the links that join them either in star or delta connection, You can def do a insulation test between L/E N/E CJS

Link to comment
Share on other sites
 
 
Mr Sworld
Phase rotation.

Be careful that it doesn't run backwards.

It's a single phase motor so hence no phase rotation!

Link to comment
Share on other sites
 
Andy™
Why would you insulation resistance test between l/N these are connected together through the windings of the motor it should come back as a short circuit!

er... if its 3 phase, you will have 3 seperate windings, each isolated from each other (until they are linked either star or delta when installed)

Link to comment
Share on other sites
 
seajayess
er... if its 3 phase, you will have 3 seperate windings, each isolated from each other (until they are linked either star or delta when installed)

If you read my whole post you will see that I state this CJS

Link to comment
Share on other sites
 