insulation test


mark303

Recommended Posts

Hi people

can anyone help with a problem insulation testing with a megger 1552

keeps coming up 000 whatever its connected to when the test button is

activated

have I broke it?

Link to comment
Share on other sites

try connecting all the leads together .. and test .. try again with all leads seperated .. what do u get ??

i can get this if the leads are not pushed in tight

Link to comment
Share on other sites

with both leads connected 000

leads seperated 299

er... your supposed to get 000 with leads touching?

Link to comment
Share on other sites

why stil 000 when connected together through a new roll of cable one clip to brown one clip to blue blue and brown together at other end

Link to comment
Share on other sites

your testing insulation between conductors. you do not short it together at any point

Link to comment
Share on other sites

you want the highest possible resistace. you do not 0 test leads for IR, but shorting them together to get 0 before a test ensures they are correctly connected to tester

Link to comment
Share on other sites

if you ir test a short piece of cable say 1mm csa would you get a reading and what should it be assuming the cables good

The Don would expect a high reading, perhaps 299.

The Godfather

Link to comment
Share on other sites

If you IR tested a brand new reel of T&E I would expect to get >299mohms on all the readings....

DO NOT CONNECT TOGETHER THE OTHER END

Link to comment
Share on other sites

If you IR tested a brand new reel of T&E I would expect to get >299mohms on all the readings....

DO NOT CONNECT TOGETHER THE OTHER END

299Mohm

The Boys

Link to comment
Share on other sites

My sincerest apologies DonBlushingBlushing

I don't know what came over me:_|, I hope (Pray) that the boys aren't on their way;)

Link to comment
Share on other sites

if you ir test a short piece of cable say 1mm csa would you get a reading and what should it be assuming the cables good

for a new cable, expect a reading higher than your test kit can measure

Link to comment
Share on other sites

so the test leads have no resistance

your testing the IR, try one clip on brown one on blue but dont join the other end.

Link to comment
Share on other sites

your testing the IR, try one clip on brown one on blue but dont join the other end.

dont forget you also need to test the earth

Link to comment
Share on other sites

Think O/P confused insul. with cont. testing.........

Link to comment
Share on other sites

Think O/P confused insul. with cont. testing.........

KME the forum was discussing your absence only the other day, hope you are well and welcome back!!

Link to comment
Share on other sites

Think O/P confused insul. with cont. testing.........

Sounds like it to me too. :)

Where have you been hiding Mate?

Great to see you back online.

Best Wishes,

Admin.

PS. I have heard from Mr Sworld, Guys - He will be rejoining us soon. Haven't heard from Steps though.

One big happy family. :D:x

Link to comment
Share on other sites

Archived

This topic is now archived and is closed to further replies.

×
×
  • Create New...

Important Information

Terms of UseWe have placed cookies on your device to help make this website better. You can adjust your cookie settings, otherwise we'll assume you're okay to continue.