summer house


sellers

Question

sellers

Just had a call from a bloke I've been doing some work for. He's a landscaper and has just put a new summer house in someone garden and wants me to wire it. He says theres already a 6mm swa put in to feed it.

I'm just after a bit of info before I go take a look, just to clarify a few things. The 6mm swa should be ok (after considering length, volt drop, etc) to suply 3 twin socket outlets, and a light. It would need RCD protection.

Only problem is, they say they would like a hot tub at a later date. Now i know nothing about hot tubs but i pressume they are a fair few KW's therefore the 6mm is only good for scrap? Whats the average kw rating of a hot tub?

Whats your best advice for feeding the summer house? come off a 40amp mcb to a small cu in the summer house? Or split tails to an isolator then off to a small cu?

Awaiting your expertise

Link to comment
Share on other sites
 

13 answers to this question

Recommended Posts

sellers

I've been looking into hot tubs and theres a whole market of them at 2kw plug and play. So hopefully he'll be wanting one of this size otherwise his 6mm isnt going to do. I just hope the 6mm is put in to the db, and not left at the back of the house for a spur which obviously wont do.

Next question. Zones. Been looking and if you class it at as a bath, then i can have rcd protected sockets 3m away, if its classed as a pool, then 2m away. But what about the spur to feed the tub? surely the flex isnt going to be 3m long?

Link to comment
Share on other sites
 
matt.leung

put the connection in zone 0. (under the tub)

Link to comment
Share on other sites
 
Andy™
put the connection in zone 0. (under the tub)

zone 0 is inside the bath. under the bath is outside the zones if a key/tools is req'd for access, otherwise zone 1

Link to comment
Share on other sites
 
matt.leung

oh ****... that was a basic error on my part..

Link to comment
Share on other sites
 
sellers

zone 1? I may want to put a masterseal spur in then if thats the case.

cheers :)

Link to comment
Share on other sites
 

'hot tubs are to be considered pools and fall under that relavent section in the regs' thats my scheme providers stand on it.

Link to comment
Share on other sites
 

I just put in a hot tub circuit - 4mm SWA; 16A rating on tub instructions. The one before this required 20A supply (via an isolator). 6mm should be fine unless the punters go for an all singin' model with inbuilt lights, sounds etc - and they usually don't when they see the price!

Link to comment
Share on other sites
 
sellers

edit* I didn't mean isolator i meant breaker.

Link to comment
Share on other sites
 
jl-heating

u should edit ur original post hehe ... then no one would know the mistake . :)

and i make loads so edit is my best friend

Link to comment
Share on other sites
 
Evans Electric

I have only done one outside hot tub , it was a 13 amp supply. In which case your 6mm would be OK.

Link to comment
Share on other sites
 
sellers

ah. but as on old spark once told me when i was a wee lad.

'a man who makes no mistakes, doesnt usually make anything' :P

either that or I didn't spot the edit button Blushing

Link to comment
Share on other sites
 
septiclecky
I just put in a hot tub circuit - 4mm SWA; 16A rating on tub instructions. The one before this required 20A supply (via an isolator). 6mm should be fine unless the punters go for an all singin' model with inbuilt lights, sounds etc - and they usually don't when they see the price!

Depends upon how far the summer house is from the main building and don't for get about the volt drop etc if it has been buried in the ground.

Link to comment
Share on other sites
 
Andy™

or as a thread the other day, the hot tub needed a 45A supply. too many variables on hot tub ratings to suggest a cable now, other than assume 60A and install for that

Link to comment