Testing a 110v Industrial Socket System


electelconnections

Question

Hi Guys,

We are completing a periodic inspection of a factory unit and have come across a transformer supplied from 1 of the DB's which in turn supplies 110v to a single phase DB which feeds 3 110v socket banks from D type DP mcb's.

We have been informed by NICEIC to test supply into transformer as a distribution circuit and test the 110v as a Db: Question is How do you perform zs test and will a megger MFT1552 perform a 110v zs test?

Link to comment
Share on other sites

11 answers to this question

Recommended Posts

Aren't these centre earth tapped to its only 55V RMS to earth? I thought the Meggers only needed over 50V to perform a test but not sure if this will work or not.

Ian.

Link to comment
Share on other sites

with it being centre tapped, it may show as wrong polarity and refuse to test. in which case you could test L1 to earth and L2 to earth and note the highest

Link to comment
Share on other sites

thanks Andy,

we tested between phases and earth and could not get a reading but when we tested between the 2 phases we got a zs reading?

Link to comment
Share on other sites

did it do a test on phase - earth?

Link to comment
Share on other sites

On a lot of these systems, the earth has to be linked during installation.

If it hasn't been linked, then you will not get a Zs reading, as there will be no continuity.

Link to comment
Share on other sites

yes we got reading between phase & Earth when doing R1&R2 but we did not get a zs result between phase & Earth but we got a result when we tested between the 2 phases?

Link to comment
Share on other sites

did the test kit actually do an earth loop between phase and earth?

Link to comment
Share on other sites

not really sure. not done much testing on 110v. if i get time, ill have a go at it tomorrow and see what i get. what did you get phase-phase?

Link to comment
Share on other sites

between phases we got 0.32 but I dont understand how we got a reading between phases as earth fault impedance surely needs to be tetsted between phase and earth?

Link to comment
Share on other sites