Another TT question


lilman

Question

Evening all - seems to be a lot of TT queries of late!? Testing today and Ze (rod resistance) of 34.0 ohms; rather good I thought - but Zs on various circuits is around 0.85 to 1.70 ohms. I presume with the main bonds to water and gas connected these parallel paths are making the readings lower - but these readings seem really low. Anyone else had this kind of caper before. Any ideas?

Link to comment
Share on other sites
 

7 answers to this question

Recommended Posts

Andy™

metallic gas/water pipe to next house, through their bonding and their PME supply.

Link to comment
Share on other sites
 
metallic gas/water pipe to next house, through their bonding and their PME supply.

Obviously the low readings are good in my customers house, but is this scenario OK as is - I presume it must be?

Link to comment
Share on other sites
 
Andy™

its safe (unless your the only house on the street with PME, and a few neighbours have earth faults and melt your earth cable!)

Link to comment
Share on other sites
 
 
 
 
it also could be showing a neutral earth fault

Please could you expand on this Cheggers? Thanks

Link to comment
Share on other sites
 