Well-known member
Was called to a job tonight on a 8.5Kw Triton shower that had completly melted on to the wall of an OAPs bathroom.
Cecked the circuit and found that it had been wired into the exsisting ring main circuit upstairs. (2.5mm) cable
It had a bs 4293 rcd at the board and on to 32 amp ring.
My question is why did the RCD no trip as this shower was instaled 12 years ago or Mcb trip due to load.
Cecked the circuit and found that it had been wired into the exsisting ring main circuit upstairs. (2.5mm) cable
It had a bs 4293 rcd at the board and on to 32 amp ring.
My question is why did the RCD no trip as this shower was instaled 12 years ago or Mcb trip due to load.