sellers

Question

sellers

Whats the best way to gland an swa into someones CU? Am i best glanding into an adaptable box and trying to bush it into the cu? You know how brittle some of them are I dont fancy glanding it straight in.

Link to comment
Share on other sites
 

25 answers to this question

Recommended Posts

sellers

My local isolator for the hot tub would be the 40a rotary one, the protection for the swa is at the cu 40amp mcb. So why would they're be a need for an isolator at the cu? I am going to put one in as I might aswell terminate my swa into it, but just curious as to why, or is it just down to good practice.

Link to comment
Share on other sites
 
Evans Electric

I wouldn't even try M8, Make gland into adapt.box, then if possible, fix the box butted against the C/U ,pass the tails through a grommet and earth lug onto the banjo.

If the cable coes outside put an isolator instead.

Link to comment
Share on other sites
 
Apache

What about a metal CU?

Link to comment
Share on other sites
 
Evans Electric

Yes , no problem if its metal, its made for the job , just bash out a 20 mm KO and Bob's yer uncle.

Link to comment
Share on other sites
 
sellers

Cu's plastic and already existing, its a feed to a summer house, does it have to go through an isolator then or is the mcb ok with an adaptable box.

Link to comment
Share on other sites
 
Evans Electric

As far as I know ,a DP isolator is required so use it to terminate and earth your SWA and tails to your C/U.

Link to comment
Share on other sites
 
Evans Electric

You would have to check the Regs on this but I was brought up with it. So if I did a garage/shed supply in SWA it would have an isolator by the board or where it left the house. Just looking at the hot tub in the same way.

Deke

Link to comment
Share on other sites
 
Andy™

but the MCB will be point of isolation for SWA. this is no different to your standard lighting circuit, just your wiring in SWA instead of T&E, and hot tub instead of light

Link to comment
Share on other sites
 
Evans Electric

The point I,m making is that it leaves the building for whatever reason so it needs to be isolated , without pratting about at the fuseboard. MCB isn't double pole for one reason , but I'm probably talking through my posterior, I don't do a huge amount of house bashing, so just use the MCB then.

Link to comment
Share on other sites
 
Andy™

i dont recall any requirement to have an isolator other than the MCB

and in commercial, do you add an isolator between MCB and SWA if taking it outside?

Link to comment
Share on other sites
 

Good morning everyone, just like to ask a question about this topic. During a recent 2391 course the subject of out buildings came up and the question of exported earths was discussed at length, the opinion of the trainer was that in some instances the outbuilding should become TT. Does this make sense or posterior talking?

Kind regards to all, have a nice weekend

David

Link to comment
Share on other sites
 
 
Andy™
Good morning everyone, just like to ask a question about this topic. During a recent 2391 course the subject of out buildings came up and the question of exported earths was discussed at length, the opinion of the trainer was that in some instances the outbuilding should become TT. Does this make sense or posterior talking?

Kind regards to all, have a nice weekend

David

PME should not be exported. TNS & TT can, although in many cases, its best to TT the outbuilding. this has been discussed in detail many times before. a quick search (if patch doesnt beat you to it) will get you lots more info

Link to comment
Share on other sites
 
Evans Electric
i dont recall any requirement to have an isolator other than the MCB

and in commercial, do you add an isolator between MCB and SWA if taking it outside?

Well yes I would, with label , such as , Scrap Paper Compressor, etc perhaps its just me making my own regs up.

Link to comment
Share on other sites
 
Evans Electric
Good morning everyone, just like to ask a question about this topic. During a recent 2391 course the subject of out buildings came up and the question of exported earths was discussed at length, the opinion of the trainer was that in some instances the outbuilding should become TT. Does this make sense or posterior talking?

Kind regards to all, have a nice weekend

David

Thought it was just me who could " Posterior Talk" Bit muffled when sitting down so always best to stand at the computer. :o:p:D

Link to comment
Share on other sites
 
Andy™
Well yes I would, with label , such as , Scrap Paper Compressor, etc perhaps its just me making my own regs up.

id have an isolator at end of SWA to isolate equipment, but thats it. but if your getting paid for it, then install it

Link to comment
Share on other sites
 
sellers

Is a DP isolator required for the hot tub circuit. Which will be a 10mm swa, from a 40amp rcd protected breaker from the house cu. With a 40a rotary isolator outside.

Link to comment
Share on other sites
 
PME should not be exported. TNS & TT can, although in many cases, its best to TT the outbuilding. this has been discussed in detail many times before. a quick search (if patch doesnt beat you to it) will get you lots more info

or me :^O

http://www.talk.electricianforum.co.uk/showthread.php?t=4444&highlight=exported+earth ;)

Link to comment
Share on other sites
 
Andy™

Still many more for patch to find!

Link to comment
Share on other sites
 
 
Andy™

So are you going to tell patch he's been made redundant?

Link to comment
Share on other sites
 
Zeespark

I would say so sellers, better to have a bit too much protection than none at all.

AndyGuiness Drink

Link to comment
Share on other sites
 
Apache
So are you going to tell patch he's been made redundant?

I don't mind. Tired tonight. Been birthing cows!

Link to comment
Share on other sites
 
Andy™

i notice i had to tell him then Badger!

Link to comment
Share on other sites
 
Evans Electric

Every appliance should have a local isolator.

Link to comment
Share on other sites
 