Shocks all round
stick probles on respecitive terminals and press test?
Link to comment
Zs is usually done at end of circuit not at dis board but maybe I am reading this wrong anyway welcome to the forum shocks all round.
Batty
Link to comment
Mains off, main bonds to services disconnected, earth croc clip on earth bar, live probe on incoming live, neutral probe on incoming neutral...... test.
Link to comment
How to get Zs at the board? i have fluke 1651 testerheadbang
Does it not come with instructions?
Don & His Boys
Link to comment
Welcome to the forum S.A,R.
Zs is performed at points around a circuit as required
Ze is performed at the incoming Supply
If it is a sub board then Ze would be classed as Zdb.
Ze [orZDB]
Perform safe Isolation .which will result in Main Isolator in OFF position.
Disconnect Main Earth conductor from Main Earth Terminal
Connect Earth lead from your tester via its croc clip to the Disconnected Earth conductor.
Connect Neutral Probe from your tester to Neutral connection of Incoming side of Main Isolator
Connect Live Probe from your tester to Line Connection of incoming side of Main Isolator
Press test on tester and note the reading...remove test leads
IMPORTANT ! Immediately reconnect the Earth Conductor to the MET..then switch isolator back on ...if required
Link to comment
Hi yer R.U.S. Just one point on your method. If earth Conductor is left connected to Earth bar there is still a possibility of parrallel paths through cpc to Extraneous conductive parts etc........what do you think ?
Link to comment
You're right lol.... I stand corrected. Proper method would indeed be to remove the earthing conductor from the earth bar.... Applaud Smiley ... (having said that I have occasionally compared the readings and there was very little difference.)
Link to comment
Your welcome R.U.S ..and thanks for not taking offence , or taking it as criticism :)
Not at all a1 :), despite being a spark for 18 years I would never claim to know it all or say I do everything right. I still make mistakes so I appreciate you mentioning it.
Link to comment
The last three posts reminds me why this is the best forum in the world!
Link to comment
Can I just add for the benefit of absolute clarity for eveyone....
all of the above guidance would assume that the POLARITY at the incoming supply has be verified prior to doing the Zs / Ze /Zdb at the board.
Although unlikely to be wrong you should NEVER assume anything is correct,
but that said ....
Most modern test meters will give some sort of error indication if polarity is arse about face!:)
Just thought I would add that in case any new starters to the world of electwickey are reading!:D:x
Sybil Fawlty specialist subject stating the bleedin obvious!Blushing:coat
Link to comment
The last three posts reminds me why this is the best forum in the world! UNIVERSE
just had to correct GH's error!!!X(X(]:)
:^O:^O
Link to comment
but that said ....
You can't say " Face" on here, Specs.!!!;)
Link to comment
OMG the last posts were that polite I thought I was living in the 1940s.
Thanks awfully chaps, I,m not taking the wee-wee by the way, TTFN .
Yours most graciously
Deke
Link to comment
Deke
Diolch yn fawr Mr Evans :^O..... respect and good manners cost nothing .... bring back the 1940's ! Applaud Smiley
Link to comment
Deke's not Welsh..............
Link to comment
Archived
  • Create New...