I have just done and passed my 2382 exam so I'm very pleased at the moment, but one of the questions I got had me stumped.
The question was.... A 3 phase motor rated at 16Kw at 400V with a full load factor of 0.8 what is the full load current ?
I didn't have a clue, and still don't. So was wondering if any of you kind people could tell me the answer and how you worked it out please.
Many thanks
Lyngarth
3 Phase circuits: Power/Square root of 3 x Voltage x PF
16000
1.73 X 400 X 0.8
= 28.86 Amps per phase
when calculating 3 phase circuits we have to allow for the effects of highly inductive/highly capacative loads therefore we use the equation above,
I hope this helps cheers (Meerkat) ;)
Sorry for the delay, been working away.
Many thanks for the replys, it easy when you know how, I have made a note of that and will keep it safe.
Cheers
Lyngarth