I have been asked to price up remedials from a pir.
The electrician who carried out the testing has put on the cert that the installation is satisfactory on the front page,but in the summary of the installation has put satisfactory once the remedials have been carried out.
1 consumer unit should be upgraded to rcd protection code 2
2 cables inside db in connector and needs repaired code 1
3 main di tails are damaged code 2
4 all wiring in consumer unit needs improvement code 2
5 no main bond to water and gas code 2
6 no hard wired smokies code 2
7 socket on landing is unswitched code 2
8 16a mcb feeding 1mm2 t&e code2/3
9 lighting circuits doubled up at db code 2
10 cooker circuit is suppling twin socket on a 32a mcb code 2
11 spur for shed is mounted surface on a flush box code 2
12 main earth has been trimmed at db code 2
13 pattress for shower is broken code 2
14 shower switch connections are exposed and require improvement code 1
15 socket in shed is damaged code 2
Dont really agree with some of the codes that have been issued,but the landlord is asking me to price up the work for him.
The testing electrician has given him a price for all of the repairs and another spark has made him aware that not all of the repairs need done,some are just going over the top.
My question is if i carried out the repairs i felt were unsafe would that be adequate or because the way the tester has worded it would all of the repairs require to be done.
The electrician who carried out the testing has put on the cert that the installation is satisfactory on the front page,but in the summary of the installation has put satisfactory once the remedials have been carried out.
1 consumer unit should be upgraded to rcd protection code 2
2 cables inside db in connector and needs repaired code 1
3 main di tails are damaged code 2
4 all wiring in consumer unit needs improvement code 2
5 no main bond to water and gas code 2
6 no hard wired smokies code 2
7 socket on landing is unswitched code 2
8 16a mcb feeding 1mm2 t&e code2/3
9 lighting circuits doubled up at db code 2
10 cooker circuit is suppling twin socket on a 32a mcb code 2
11 spur for shed is mounted surface on a flush box code 2
12 main earth has been trimmed at db code 2
13 pattress for shower is broken code 2
14 shower switch connections are exposed and require improvement code 1
15 socket in shed is damaged code 2
Dont really agree with some of the codes that have been issued,but the landlord is asking me to price up the work for him.
The testing electrician has given him a price for all of the repairs and another spark has made him aware that not all of the repairs need done,some are just going over the top.
My question is if i carried out the repairs i felt were unsafe would that be adequate or because the way the tester has worded it would all of the repairs require to be done.