ir on ring main


tom1

Question

insulation test on ring came up with 59M ohms

looked at his last nic eice cert dated 2 year back he got 200M ohm

its the old stranded cable i advised he should replace it befor he decorates.

thats a big deteriation i wonder if the last guy even did the test and why he left in the stranded cable

Link to comment
Share on other sites
 

7 answers to this question

Recommended Posts

 

the cu was a bit strange as well,

rcd, 2 16a radals 1 socket each,

1 16a garage,

32a cooker,

every other socket on 32a,

non rcd

light circits

and a 50a shower :|

Link to comment
Share on other sites
 

tom there is nothing wrong with the ir its well within the 1meg allowed. this reading could indicate dampness in the walls, something plugged in.I would only start to worry when it gets to 2 megs

also nothing wrong with stranded

Link to comment
Share on other sites
 

yer it just seemed a big drop for 2 years but like u say could be damp. i did my best to unplug everything but its always a pain when its not a new installation, i did p+n to earth just in case i missed something.

just the shower i recomended an rcbo, they are always tight though,

Link to comment
Share on other sites
 

Did you test it 2 yrs ago when it was >200M? If not, I would be dubious about the reading. I have come across situations where the readings are falsely put down;) Nothing wrong with 59M though. Not brilliant but hey, the cables are donkeys yrs old.

Link to comment
Share on other sites
 
Revved Up Sparky
yer it just seemed a big drop for 2 years but like u say could be damp. i did my best to unplug everything but its always a pain when its not a new installation, i did p+n to earth just in case i missed something.

just the shower i recomended an rcbo, they are always tight though,

Hi Tom, should'nt the lights go on an RCBO too ? (17th ed)--- or maybe the cables are buried deeper than 50mm etc.

Link to comment
Share on other sites
 

Revved, ideally all circuits should be RCBO protected, only problem is, as you know, they cost a small fortune each.