6mm shower


musicspark

Question

I have been asked to reconnect a shower which was installed "two or three years ago"

The customer is therefore reluctant to believe there can be anything wrong.

The shower is a "Myra Sport" on a 6mm cable It has a nice Merlin Guerin RCD next to the CU but on a 40A breaker. I realise that something has to change but I don't know the rating of this model of shower can anyone help?

Link to comment
Share on other sites

  • Answers 55
  • Created
  • Last Reply

Recommended Posts

Mira Sport come in a range of sizes. Often it will be Mira Sport 7.5 etc

:)

Link to comment
Share on other sites

I don't mean it's a 7500W I mean there is a number that will say

:)

Link to comment
Share on other sites

Thanks Apache,

But that don't help much do it?

do you know if there is a plate anywhere inside this appliance which would give me the info ; or do I have to use a bag of bones to determine the wattage?

Perhaps a spiritualist or soothsayer? ;\

Link to comment
Share on other sites

Thanks Apache,

But that don't help much do it?

No. :)

Have you taken the cover off? No rating plate inside?

If you've got a clamp meter turn the other breakers off, whack it around a meter tail and measure it?!

Link to comment
Share on other sites

your way ahead of me Apache ,but the shower is not connected ,and there is as yet no wall for it to fix on to or bath for it to run into

:|

Link to comment
Share on other sites

what are u worried about puting the wrong size mcb

or cable melting?

Link to comment
Share on other sites

I have been asked to reconnect a shower which was installed "two or three years ago"

The customer is therefore reluctant to believe there can be anything wrong.

The shower is a "Myra Sport" on a 6mm cable It has a nice Merlin Guerin RCD next to the CU but on a 40A breaker. I realise that something has to change but I don't know the rating of this model of shower can anyone help?

Not sure why you are saying something has to change??

any way...

as Apache said.. Mira Sport? what power rating is it?

e.g...

http://www.mirashowers.co.uk/onlinecatalog/results.htm?sectionName=Electric showers&filter[bRAND_NAME]=Sport

6.0mm cable, clipped direct could carry 47Amps...

table 6F page 134 on-site guide..

And according to table 7.1 page 50 on-site-guide

a 40Amp 6.0mm circuit (inst method C) can be upto 40m long!

so 40amp MCB could provide power for 40x230 = 9.2kWatt.

So if your cable is clipped direct, the run is less than 40m

and the shower is 9.0kw or less...

what needs to change??

Link to comment
Share on other sites

there should be something that gives a rating.........

sticker on the back? model number you can google?

Link to comment
Share on other sites

what needs to change??

Underpants? Might get hit by a bus?

:D

Link to comment
Share on other sites

what it if turns out to be a 10.6kw shower

or a sandwich toaster?

We need facts here!

Link to comment
Share on other sites

what it if turns out to be a 10.6kw shower

tell em to take it back and get a smaller rating model..

or pay for cable upgrade!

10600/230 = 46+ amps...

IMHO 10.0mm & 50A MCB:);)

Link to comment
Share on other sites

Underpants? Might get hit by a bus?

:D

only change underpants Wednesdays & Sundays!!!BlushingO)

don't we all do that?:|?:|

or has Deke been tellin me stories again:(:_|

Link to comment
Share on other sites

i dont follow

We need leaders in life.........

:coat

Link to comment
Share on other sites

Not sure why you are saying something has to change??

any way...

as Apache said.. Mira Sport? what power rating is it?

e.g...

http://www.mirashowers.co.uk/onlinecatalog/results.htm?sectionName=Electric showers&filter[bRAND_NAME]=Sport

6.0mm cable, clipped direct could carry 47Amps...

table 6F page 134 on-site guide..

And according to table 7.1 page 50 on-site-guide

a 40Amp 6.0mm circuit (inst method C) can be upto 40m long!

so 40amp MCB could provide power for 40x230 = 9.2kWatt.

So if your cable is clipped direct, the run is less than 40m

and the shower is 9.0kw or less...

what needs to change??

Yes but the cable is also ru through a loft with rockwool insuation which would surely derate the capacity of the cable?

Link to comment
Share on other sites

should be a serial number, to ring up or look on web

special a question, say the appliance was put on a 6mm 45amp mcb and the appliiance draws 51 amps, 6 extra amps i dont think will trip any time soon. will it be a prob on the cable or will it take it untill the mcb trips

Link to comment
Share on other sites

Yes but the cable is also ru through a loft with rockwool insuation which would surely derate the capacity of the cable?

Why not share this info in OP?

X(

Link to comment
Share on other sites

Archived

This topic is now archived and is closed to further replies.



FORUM SPONSORS

Test Equipment Manufacturers
Electrical & Tool Suppliers
Tool Manufacturers
Electrical Software
Education & Training
To Advertise and become a Forum Sponsor of

talk.electricianforum.co.uk, please

contact the Administrator

Here Thank You.




×
×
  • Create New...

Important Information

Terms of UseWe have placed cookies on your device to help make this website better. You can adjust your cookie settings, otherwise we'll assume you're okay to continue.