spurs spurs spurs


sellers

Question

If a fused spur is on the ring circuit. can I add another fused spur onto this?

Why I ask is, I've been rewiring the socket circuits at a property and a shed on the side of the house is off the upstairs ringmain, (conduit out of back of a bedroom socket outside then bend down into shed. 2 sockets, sfcu for single light.

I wanted to add a fused spur onto the ring next to this socket and come out of this into the shed.

Link to comment
Share on other sites

9 answers to this question

Recommended Posts

If you have got a fused spur then you can add as many sockets as you need from this, however being sensible you will be restricted by load and cable length due to Vd.

However Sellers can you clarify -

1.are you intending in taking two spurred radial ccts from one socket outlet point? Cos this would be against regs.

2. the original fused spur is wired into the ring and you want this to feed 2 radials into the shed..why would you want to do this?

3. I think you are saying that at present a spur is taken from a bedroom socket which is not fused down and is supplying 2 socket outlets and a lighting cct. So you want to rectify this by installing a SFCU, then yes this is better solution. However what about RCD protection as might need RCD protected SFCU.

Link to comment
Share on other sites

If a fused spur is on the ring circuit. can I add another fused spur onto this?

Why I ask is, I've been rewiring the socket circuits at a property and a shed on the side of the house is off the upstairs ringmain, (conduit out of back of a bedroom socket outside then bend down into shed. 2 sockets, sfcu for single light.

I wanted to add a fused spur onto the ring next to this socket and come out of this into the shed.

Absolutely nothing wrong with what you propose. The fuse in the first fcu will protect everything downstream against overload. As mentioned above look our for volt drop and Zs, although I assume it will be rcd protected.

Link to comment
Share on other sites

If a fused spur is on the ring circuit. can I add another fused spur onto this?

Why I ask is, I've been rewiring the socket circuits at a property and a shed on the side of the house is off the upstairs ringmain, (conduit out of back of a bedroom socket outside then bend down into shed. 2 sockets, sfcu for single light.

I wanted to add a fused spur onto the ring next to this socket and come out of this into the shed.

if the fused spur is wired as part of the ring (i.e doesnt have a single feed to it from another socket), then yes, you can take a spur from it. its no different from taking a spur from a socket.

Link to comment
Share on other sites

spurs.jpg

This is what i propose.

The bottom bit is the ringmain. Originally it was just a socket on its own.

edit* its really small. On the doubles it says SO, and on the singles 13a FCU and 5a SFCU

Link to comment
Share on other sites

Assuming the spur is wired in 2.5 (upto the second FCU) that's fine

Link to comment
Share on other sites

i would agree thats ok as the first 13a fcu will be protecting the sockets and sfcu beyond it. will it be clipped direct? just wonder because i would have thought 1.5mm2 T&E would be fine from 13a fcu onwards. obviously depending on the distance covered,

wayne

Link to comment
Share on other sites

nothing wrong with your diagram

Link to comment
Share on other sites

Looks OK to me , Sellers, as said , everything on the spur is protected by the fuse in the FCU .

Deke