DONT STAY LURKING AS A GUEST,
CLICK HERE TO JOIN.
Tt testing
danny7299
hey up all
I have seen this somewhere , but don't know where...
on the test cerificates, on a TT system , where it says max ZS .. do you put 1667ohm ?
thanks
Link to comment
yes
Link to comment
hey up all
thanks
yes
phtt!!!:_|:(
He's a lazy barsteward that Andyc is :o:|
But he knows that some other poor sod will come and do the rest of the typing hes to lazy to add!!!!
The rest of his sentence should of read..
"Yes" if its a 30ma RCD!, but 500ohm if a 100ma RCD.
and to clarify
loads of TT installations installed PRE 17 edition would have a split load configuration with...
100ma RCD main switch, and 30ma RCD protecting only selected circuits!
So all of the 30ma RCD protected circuits would have 1667ohm max Zs
and the circuits only protected by the 100ma RCD would have a max Zs of 500ohms.
e.g.
consider illustration Figure 3.2 on page 24 of on site guide.
So if you were doing a PIR on old 16th edition TT
or 17th edition TT with some circuits in earthed metal conduit.. etc..
the blanket 1667ohm figure would be incorrect.
And anyway Danny-boy
we all know that you knew the answer to this question was on
Table 41.5, page 50 of BRB, (part of Reg 411.5.3)
and it all revolves around the 50v 'touch voltage
as per bullet point (ii) where it states:- Ra x In equal to/less than 50v
e.g.
30ma RCD: 50v/30ma = 1667ohm
100ma RCD: 50v/100ma = 500ohm.
I just think that both of you Danny & AndyC are a couple of Very Very naughty boys!!!!X(
Not doing your homework proper!!!!]:)
I shall have words with Admin & get you both put on washing up duties for the rest of the week!!!!;\X(
:^OROTFWLROTFWLROTFWLROTFWL
Blushing:x
:coat
Link to comment
i knew it would be in the book somewhere... but it was late and was easier just to ask the question!!!
i hate washing up!!! Andy C can wash and i will Dry
Link to comment
ill wash up. with C4.
Link to comment
Archived
  • Create New...