Tested two circuits today and all was ok until RCD trip times. On x5 The reading was 11ms. However, on x 1 it was showing >300ms. Is this a fail on an EIC?
On a 30mA RCD / RCBO shouldn't they be...i would think its a fail, its 200ms for the bs4293 and 300ms for bs61008
On a 30mA RCD / RCBO shouldn't they be...x
On a 30mA RCD / RCBO shouldn't they be...x
You don't do things by halves! If an old lady calls you out to replace a lamp outside you rewire the lighting circuit............Thanks chaps, have decided to change the CU tomorrow so hopefully this will rectify things.
And put in underfoor heatingYou don't do things by halves! If an old lady calls you out to replace a lamp outside you rewire the lighting circuit............
You havent got a Time Delayed RCD in the circuit have you?Tested two circuits today and all was ok until RCD trip times. On x5 The reading was 11ms. However, on x 1 it was showing >300ms. Is this a fail on an EIC?