Good morning Guys,

Does anyone have access to a table that gives the R1+R2 value per meter of copper conductors at 70mm 70mm as per table 1A in GN3 which only goes up to 50mm?

Thanks in advance for any help/ information given.

 
The list you want is in the back of the BRB.AndyGuinness
For resistance values (R1+R2)? Unless I am missing something (very possible!) the ones at the back of the Regs are for volt drop and current carrying capacities.

 
table 9A in the on site guild only goes up to 50mm but if you do what others have suggested the figures are all nearly the same 0.262 milliohms per meter for r1

 
For resistance values (R1+R2)? Unless I am missing something (very possible!) the ones at the back of the Regs are for volt drop and current carrying capacities.
Fraid you are there AndyD...

Its page 166, table 9A, you missed.

Tip of the day.....

when you find useful pages & tables...

write a note in the back of your On Site Gude... or regs book..

on those blank white pages that say NOTES at the top!

helps find thing again you use frequently...

e.g.

I have written lines such as...

Resistance/M Pg 166 Table 9a

Voltdrop/M Pg 133 Table 6E2

Max Length Std'd Circuits Pg44-> Table 7.1

etc..

etc..

In the back of my On site guide...

It all helps!

;) :x

 
Don't want to be pickey, but page 166 of the Regs. doesn't have any tables at all.

All it has is Regs. refering to special locations containing baths or showers.

 
Don't want to be pickey, but page 166 of the Regs. doesn't have any tables at all.All it has is Regs. refering to special locations containing baths or showers.
PICKY?

:eek:

Looks more like 110,000,000% correct there Spin! :Applaud :Applaud:Applaud

Twas 'On site guide' I was refering to m8 ;)

Looks like the ole incholic affluencies are working again...

GuinnessGuinnessGuinnessGuinnessGuinness

:| :p :Blushing

Do you think I should have said On-Site-Guide???

maybe?

:| :OB-) :innocent

ROTFWLROTFWLROTFWLROTFWLROTFWL

 
The Draka "cable and table" handbook gives 0.268mohm/m for 70mm.

The Draka figures agree with table G2 for all sizes.

Interestingly, the Draka book gives differing values for armoured cable according to whether it's ac or dc (higher values for ac, with the dc values being as per G2).

 
One thing is the skin effect.

Another is as follows

The a.c. values are due to the impedance and capacitance of the cable. With d.c only the resistance is relevant.

We can only measure the d.c. component with our testers so the IET only provide this value to compare to.

No EM Theory paper on a Friday night I'm after a few Guinness

Paul

Edited for better explanation.

I hope!

 